Discuss Bathroom extractor fan won't work but... in the DIY Electrical Advice area at ElectriciansForums.net

nick p

DIY
Reaction score
1
I've installed a replacement bathroom extractor fan. Pic on the left is the old one. Pic on right is the new one. Wired the same way but the fan won't work when the bathroom lights are switched on. But if I put a multi meter on the Switched Live & Live terminals, it starts working. Is the fan faulty?
 

Attachments

  • IMG_20230930_122304433.jpg
    278 KB · Views: 16
  • IMG_20230930_130338507.jpg
    394.4 KB · Views: 16
The terminal block looks like it has partially come away from the circuit board, the terminals are soldered in place and I suspect at least one is broken. You applying pressure with the test leads is making them contact again.
 
Last edited:
The terminal block looks like it has partially come away from the circuit board, the terminals are soldered in place and I suspect at least one is broken. You applying pressure with the test leads is making them contact again.
Thanks. I wondered that as the connection block is at an angle. I'm going to replace the whole thing I've decided.
 
The terminal block looks like it has partially come away from the circuit board, the terminals are soldered in place and I suspect at least one is broken. You applying pressure with the test leads is making them contact again.
Bad news. I bought a replacement fan. Wired it in just like the first one and it's doing the same thing. If I bridge the Live and S/Live terminals with the multimeter, it worked. I know the isolator switch works as I tested it.
 
Check the connections at the isolator and the connections at the lights.
 

Reply to Bathroom extractor fan won't work but... in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
368
HI There, I would be grateful if you could help me, I have a very long duct between the bathroom and extractor outlet vent and for sometime, the...
Replies
3
Views
1K
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
250
Hi Just replaced a bathroom extractor fan. I didn't alter any wiring. Both old & new have live & switched live. Trouble is, once activated, the...
Replies
5
Views
340
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock