Discuss Bathroom Extractor Next to Shower Head in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
2
Doing an Eicr and the 230v timed class 1 bathroom extractor is less than 200mm next to the shower head.

I see this as a C2 and would insist on it being changed to at least a 12v fan or even better a new location.

Welcome any thoughts
 
There are some fans that are rated for such a zone at 230v. But if not then I agree with your coding. Is it actually in zone 1? Personally I would defo go for the 12v fan as standard in such a situation.
 
Is it zone 1 or high enough to be out of zones?
What IPX rating does the fan have?

IPX4 rated mains voltage ventilation equipment would be allowed in zone 1.
 
I have no information on the fan, i dont think its a zone 1 fan as its open and has a pull cord.. change for zone 1 fan.. sometimes you just know, but just need that someone to bounce ideas off. Thanks
 
I entirely share your concerns about that.
Generally stuff in zone 1 would need to be IPX4. I'd argue that this is easily exposed to water jets and the extra sentence in the regs applies, so even though it's in zone 1 the fan should be IPX5 rated.

It doesn't 'look' as though it's built to withstand water jets from any direction, and I'd agree with C2.
 
I entirely share your concerns about that.
Generally stuff in zone 1 would need to be IPX4. I'd argue that this is easily exposed to water jets and the extra sentence in the regs applies, so even though it's in zone 1 the fan should be IPX5 rated.

It doesn't 'look' as though it's built to withstand water jets from any direction, and I'd agree with C2.
Thanks Tim,
Totally agree, definitely dosn't withstand water jets. i know that some manufactures zone 1 fan yet still have guidance to be 300mm from water jets, so IPX5 is good call for that
 
Devils advocate…. C3, improvement recommended.

Definitely zone 1 if it’s directly above the shower tray….

How “potentially dangerous” is it?

It gets wet, it should trip the rcd…. Unless that’s not in place??
 
Reading the reg, and the IP ratings, I think 'spray from showers' isn't as severe as 'water jets'. Otherwise we'd need IPX5 shower units?
It's a good point that some showers are IPX4.
I noticed the previous sentence in the regs mentioned "spray from showers" when talking about shaver sockets in zone 2.

Yet (ignoring regs a minute) if we also think about IPX4 being "water splashed against the enclosure" and IPX5 being "water sprayed in jets" I think this does fall somewhere in the middle. The shower could be accidentally aimed straight into the fan quite easily which exceeds splashing really.

Maybe it's wrong to say IPX5 is required by regs, and it more highlights that the fan in question can't be IPX4. Looking at other IPX4 fans online they all look a lot more able to withstand shower spray than the one above!
 

Reply to Bathroom Extractor Next to Shower Head in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
632
My extractor fan has given up the ghost this week and I was hoping to replace it myself, however I cannot do a like for like swap as the current...
Replies
1
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet...
Replies
31
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock