Discuss Bathroom led strip query in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
73
Had to remove a led strip from a bathroom today because it’s getting tiled, now the led strip that was there was low voltage but didn’t have anything covering it. I’ve seen the wee aluminium profile things before, is this something that the led strip should be fitted in when in a bathroom? It was fitted in a wee alcove type bit and wasn’t really able to be touched as such. Only ever done one before in a kitchen
 
Had to remove a led strip from a bathroom today because it’s getting tiled, now the led strip that was there was low voltage but didn’t have anything covering it. I’ve seen the wee aluminium profile things before, is this something that the led strip should be fitted in when in a bathroom? It was fitted in a wee alcove type bit and wasn’t really able to be touched as such. Only ever done one before in a kitchen
Some LED strips, typically those IP rated, have a silicone covering moulded on and can be used in bathrooms as they are.
If your strip is like that then the profile is really just for looks.

If your strip is driven from a Class III separated extra low voltage driver, (it would have SELV written on it) then even if the strip has 'bare' components and copper, I don't think profile is required by regulation, but you might choose to use it again for looks and protection from splashes!
 
The Schluter LED strips come in up down or straight emitting lights and have cutting marks where they can be shortened, they also come with a silicone compound and end cap to maintain their IP rating, can't recommend they highly enough.
 
It is expensive, but you get what you pay for, they replaced a faulty transformer free of charge and did not ask for the old one back before they would send out the replacement to France, so not inexpensive for them, makes a change for someone to stand by a guarantee no questions asked.
 
You can buy Aluminium profile on 1 metre lengths from any wholesaler, and possibly online cheaper from that south American river place.

I buy standard profile from Amazon, which is identical to that offered by local wholesalers and considerably cheaper. The only discernable difference is delivery from Amazon is 1m lengths, whereas wholesalers stock 2m lengths.
 
I did LED tape for a customer around the shelves of his “media wall”
Got it from CEF, along with 1m lengths of profile and cover.

And I can’t really say there’s much of a quality difference between it and the cheap stuff from Amazon.

The little flat remote control is near identical.


I put cheap stuff under the shelves in the back of my van, Bluetooth controlled from my phone and changes in time with music….

Disco van!
 

Reply to Bathroom led strip query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning all, Hope you’re weekend is good so far. Little question on some LED strip?? I’ve never worked with LED strip before so not really...
Replies
4
Views
3K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
449
Hi - looking for opinions please so that I respond reasonably rather than as I would actually want to. Had a towel rail in bathroom. Replaced it...
Replies
2
Views
997
Moved into a refurbed flat a couple of years ago and there were a few suspect things about the electrical work which I’ve not got round to...
Replies
8
Views
2K
Hi, I’d really appreciate some advice or suggestions as to what could be causing an ongoing issue I have with my RCD tripping. My RCD trips when...
Replies
1
Views
856

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock