Hi,

I'm looking for some guidance from more experienced hands. Have a friend who just bought a 2.2kw air compressor which is obviously blowing the fuse in the plug due to the start-up current. Manufacturers information suggests a 30a single phase motor DOL for the power rating whilst the person who sold it said it needs a 15a fused spur.

The compressor won't be installed on its own circuit with a type c circuit breaker so wondering what the best route to take given a fused spur off the ring is limited to 13a also? Someone suggested an unfused spur to a 16a single phase 2P+E connector and plug like you see at caravan parks which could cope with the start up current but any guidance much appreciated.
 
A little confused here, you say the manufacturer suggest fitting a DOL starter, doesn't this compressor already contain its own integral control?... or am I getting it wrong, a 2.2 kw single phase would have the effective inrush of a 5.5 to 7.5 kw 3ph so yes a 30amp front end type c would be recommended although you could use a permanent 16amp connection.
 
The Hager commercial catalogue (I happen to have to hand) has 2.2kW DOL single phase protection as 50A C/D MCB, or 40A fuse. Pretty brutal!
 
I agree but he sort manufacturers guidance which usually refines the worst case scenario those charts are based on. The higher the mcb the more problematic complying with ELI which makes advice difficult without having more info.
 

Reply to Best way to connect up air compressor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Bought an air compressor at auction. Looks to have been previously hooked up in the previous owners shop. It has two wire Romex coming from the...
Replies
2
Views
622
I am back to try and hook up my Frankenstein compressor. 60 gal tank, Ebay 5hp motor, HF 5 HP, 145 PSI V-Style Single Stage Cast Iron Air...
Replies
0
Views
534
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
682
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock