Search for tools and product advice,

Discuss Bizarre voltage readings in the UK Electrical Forum area at ElectriciansForums.net

G

Gossy

I have installed a new cooker supply to the new DB. The cable is a 10 mm T+E. It's on a 50 amp RCBO. (Big cooker!!) tested the cable and made put it in connector block and switched it on. I was getting 240v down live to earth which is correct but neutral to earth is was getting 40v. Then live to neutral I was getting 118V . I thought it was thought it was the RCBO but changed it three times and still read the same. When I connected it to cooker I get 240 v through neutral and earth as well as live and earth. What's going on???
 
Hi Guys, between N+E the max voltage should be at max 2V, so this sounds very much like a broken neutral somewhere or a badly connected neutral at the CU. my first test would be to check this out. I have this as a common problem here in Africa, especially when we have to use auto transfer switches between the mains incomer and the standby generator and the contacts become pitted and carbonized. So turn off each circuit at the CU, then test for a V between N+E, if it has stabilized and you are getting the correct readings turn on each circuit one by one until you identify the circuit that is giving you the problem.
Hope this helps.
 

Reply to Bizarre voltage readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
749
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
589
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Replies
1
Views
335

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock