There's some really clever people on this forum. I had to Google the electronic references, and, after reading them for a few minutes, I realised I was mentally debating tea or coffee to start the day (I went for tea).
So I can't help you there. But I will try to using my old favourite, Ockhams Razor ie go for the bleeding obvious.
Lights flickering, different flats affected, electronic gizmos feeling unwell (my knowledge of such things shines). And all about the same time.
It stinks of a neutral connection. It's the only common denominator. I can't see 11 Sangamo clocks packing up at the same time (Greenbrook, maybe..)
I was (un)lucky enough to see a neutral on a three phase supply go AWAL first hand ('tis a long story) and it is frightening. Voltage between phase and (apparent) neutral 270. Nope, 370. Nope 300. Nope 280 etc. Modular fittings jumping up in the suspended ceiling. Vending machines dying in agony.
Ok, this was for a period of minutes. Bit it's proof that the voltage goes crazy with a naughty neutral. It may be the case that your neutral was just a bit cheeky and went missing for a second or so.
One to watch out for.
So I can't help you there. But I will try to using my old favourite, Ockhams Razor ie go for the bleeding obvious.
Lights flickering, different flats affected, electronic gizmos feeling unwell (my knowledge of such things shines). And all about the same time.
It stinks of a neutral connection. It's the only common denominator. I can't see 11 Sangamo clocks packing up at the same time (Greenbrook, maybe..)
I was (un)lucky enough to see a neutral on a three phase supply go AWAL first hand ('tis a long story) and it is frightening. Voltage between phase and (apparent) neutral 270. Nope, 370. Nope 300. Nope 280 etc. Modular fittings jumping up in the suspended ceiling. Vending machines dying in agony.
Ok, this was for a period of minutes. Bit it's proof that the voltage goes crazy with a naughty neutral. It may be the case that your neutral was just a bit cheeky and went missing for a second or so.
One to watch out for.