Discuss Block of flats, supplies to flats. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi Guys,

We are undertaking a large development and just want to get some ideas on how others would supply each unit. There will be a rising main, with potentially a rhyfield unit on each floor in each 'zone'. We have in past projects used SWA to supply each unit, with the rhyfield unit supplying the redhead fuse, then supplying the meter, then supplying a switch fuse with the SWA Glanded in supplying the DB board in the flat.

With this project being slightly larger, we want to try and avoid using SWA and wondered if split concentric cable would be able to be used in this instance / how other people have supplied flats on larger scale projects.

Thanks.
 
Split concentric is commonly used for this job but it has to be protected against penetration damage: either by being in an obvious place (surface mounted or in trunking) where nobody could be expected to accidentally nail it, or is has to be greater than 50mm from any surface likely to be nailed.

SWA has the advantage of not needing 30mA "additional protection" RCD wherever it is routed (that would be unacceptable for the supply to a whole flat) subject to the usual aspect of armour being earthed and able to disconnect on faults under 5s, etc. But you have the issue of proper cable glands for that armour-earthing, stiffer cable, and slightly poorer bend radius from generally being thicker.

As a rule-of-thumb minimum cable bend radius is often 8 * cable diameter, but you should check the manufacturer's data sheet before depending on that sort of value.
 
Genuine question - is splitcon actually cheaper these days? About a year ago I considered it for a job and I seem to recall it costing about twice the price per meter as equivalent 3 core SWA.
A quick glance on CEF seems to confirm this is still the case, £9.35/m ex vat for 10mm split con, £4.80/m for SWA.
Or are there other sources where it is actually cheaper, as it logically should be?
 
Good question about the cable cost, you would expect it to be cheaper than the same 3C SWA as same copper but no armour so less manufacturing and shipping costs.

But I have never seen it as saving anything on the usual web sites. I can see how it is easier to work with and on the DNO side with TN-C (not split) even more of an advantage.
 
Did a huge amount of street lighting installs where 16mm split con was specced om nearly every job for about 4 years until 2016. Absolute pain to get 2 and sometimes 3 into a cutout inside the door, hated it since then. Swa every time, even if it was double the price
 
Good question about the cable cost, you would expect it to be cheaper than the same 3C SWA as same copper but no armour so less manufacturing and shipping costs.

But far more 3c SWA is used by the average electrician than splitcon, so your usual wholesalers will be buying far more SWA so will get far better prices on it.

It's economies of scale in action.
 

Reply to Block of flats, supplies to flats. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
822
Hi all, I hope you could share your experience and advice regarding supply 50 flats in 5 storey block of flats. We get 3 x 430A supply. What...
Replies
4
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock