I am using a 160watt-200watt multi uv tube stand alone sunbed,When the 2 power leads (plugs protected by 2x13amp fuses) plugged into a double wall socket (protected 32amp circuit breaker)the sunbed works as it should,When an extension cable with one plug top (protected by 1x13amp fuse)and 1xdouble socket is used the sunbed works for 4 mins then the 13amp fuse on extension cable plug top blows ,Can anyone explain why the 13amp fuse does not blow immediately when first switched on,
 
Quiet Simpley, the device uses more power than can be supplied by a 13A plug.
therefore the manufacturer has put 2 separate plugs on it to share the load.
 
160W-200W

Is this per tube? If so, how many tubes?
Well done it is so obvious now you have explained it’s per tube and it’s 24 tubes so that explains why the single 13amp fuse blows but why does it not blow immediately but works for 4 mins then blows ,sorry not up on theory of how uv tubes function,ps:-All 24 tubes are switched on simultaneously.
 
It's potentially running slightly over the rating of a standard double socket.

Presumably this sunbed has a rating plate somewhere on it? It would be helpful if you could provide details from it or, even better, an image of it.

I would assume that inrush current from the tubes isn't sufficient to blow a 13A fuse instantly, but load of 3.8-4.8kW explains why it doesn't hold for long as you'll be drawing somewhere between 16.5A and 20.85A.
 
It's potentially running slightly over the rating of a standard double socket.

Presumably this sunbed has a rating plate somewhere on it? It would be helpful if you could provide details from it or, even better, an image of it.

I would assume that inrush current from the tubes isn't sufficient to blow a 13A fuse instantly, but load of 3.8-4.8kW explains why it doesn't hold for long as you'll be drawing somewhere between 16.5A and 20.85A.
Rating plate has max 5kw
If this is not enough info I will send an image
 
It's potentially running slightly over the rating of a standard double socket.

Presumably this sunbed has a rating plate somewhere on it? It would be helpful if you could provide details from it or, even better, an image of it.

I would assume that inrush current from the tubes isn't sufficient to blow a 13A fuse instantly, but load of 3.8-4.8kW explains why it doesn't hold for long as you'll be drawing somewhere between 16.5A and 20.85A.
I understand the why and the how thanks to your explanation .
Thanks again for your help,The next time somebody asks me why this happens I’ll be able to sound extremely intelligent,lol
 
Rating plate has max 5kw
If this is not enough info I will send an image

That's about right - I was working on max 4.8kW @230V.

Take a look at a graph detailling operating characteristics for BS1362 fuses.

At just over 20A I'm surprised it blows so quickly. This sort of overload is more likely to generate sufficient heat to damage plug, socket and cable, but I wouldn't have expected the fuse to blow within 4 seconds. It's a fairly dangerous set up.
 

Reply to Blown 13amp fuse on extension lead in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Here's a Sunday puzzler for you all..... I've a large rental stock of properly made up mains adaptors for use in Europe and elsewhere - so...
Replies
9
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I Knew it was going to be one of those days when my first customer couldn't understand why his 9.5kw standalone oven/hob kept cutting out because...
Replies
9
Views
2K
Hi All We are currently waiting for some work too be done on the incoming supply by the DNO so have had to purchase a ev granny cable to use for...
Replies
15
Views
3K
I let out a flat and had an EICR, carried out, to meet the new Private Rented Sector Regulations. The EICR has recorded a “C2” for an extension...
Replies
34
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock