Discuss Boiler fuse/cable in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi , looking for some advice or if my question is correct please from you pros.

so my worcestor combo boiler (for few years) is fed of a 0.5mm flex from a spur, which is around 4 metres from my boiler, and has a 5amp fuse in the pull out of the spur.
ive researched and it should have a 3amp in it ideally, so my question is do cables pull more than the maximum load the experts say? Or is it because I’m guessing the tolerance of the 3amp fuse and the 5amp fuse is minimal? I know it would be silly to have a 13amp fuse put in the spur, but it seems all well and good and never any issues with the 5amp.

I know now minimal flex is 0.75mm, I researched this.
should I change to a 0.75mm flex?

thanks guys
 
Hi , looking for some advice or if my question is correct please from you pros.

so my worcestor combo boiler (for few years) is fed of a 0.5mm flex from a spur, which is around 4 metres from my boiler, and has a 5amp fuse in the pull out of the spur.
ive researched and it should have a 3amp in it ideally, so my question is do cables pull more than the maximum load the experts say? Or is it because I’m guessing the tolerance of the 3amp fuse and the 5amp fuse is minimal? I know it would be silly to have a 13amp fuse put in the spur, but it seems all well and good and never any issues with the 5amp.

I know now minimal flex is 0.75mm, I researched this.
should I change to a 0.75mm flex?

thanks guys
Can I also add sorry, the circuit it is on with is the upstairs sockets on a 32amp MCb in the fuseboard, so it’s got a 2.5mm cable feeding my boiler spur.
‘thanks
 
The two concepts are
1) how much current is the appliance drawing in normal use
2) in fault conditions will the fuse blow before the flex melts or the appliance becomes damaged.

0.5mm flex is rated for 3 amps. Your current fuse is 5 amps. So irrespective of the load (the boiler) that isn't great as the fuse doesn't protect the flex.

As main priority I'd stick a 3 amp fuse in.
 
As above, under overload conditions (less likely here) a 5A fuse is too large, but under a hard fault condition it would clear fast enough so the cable is not overheated.
 
Thanks guys, may as well change it To a 3amp then, il get one.
is it true that cables can actually take more than is stated in books (although obvs you stick to the guidelines, but are these guidelines worst case? so They can be slightly understated so people don’t abuse rules?

and if the boiler permanently works fine say forever there would never be an issue with that cable?
ive been trying to research it all and I don’t think 0.5mm has often been used in boilers for years standard practice would be 0.75mm and upwards, would that be correct?

thanks again
 
Cable ratings are not simple as you have three limits:
  • Current carrying capacity, based on maximum safe insulation temperature
  • Voltage drop, a factor for long lengths
  • Fault clearing time, so safe disconnection in under (typically) 0.4s
The first of these depends on the cable (resistance and type of insulation) but also its environment, so the ambient temperature and the level of thermal insulation around it. For critical applications you can look up the various factors and apply them, but for most cases there are simple safe guide lines.

Check the boiler spec, if it is no more than 3A then no problems!
 
Cable ratings are not simple as you have three limits:
  • Current carrying capacity, based on maximum safe insulation temperature
  • Voltage drop, a factor for long lengths
  • Fault clearing time, so safe disconnection in under (typically) 0.4s
The first of these depends on the cable (resistance and type of insulation) but also its environment, so the ambient temperature and the level of thermal insulation around it. For critical applications you can look up the various factors and apply them, but for most cases there are simple safe guide lines.

Check the boiler spec, if it is no more than 3A then no problems!
The actual glass fuse in the boiler is 1amp, so I’m guessing it’s never going to pull anything more than that anyway
 
Cable ratings are not simple as you have three limits:
  • Current carrying capacity, based on maximum safe insulation temperature
  • Voltage drop, a factor for long lengths
  • Fault clearing time, so safe disconnection in under (typically) 0.4s
The first of these depends on the cable (resistance and type of insulation) but also its environment, so the ambient temperature and the level of thermal insulation around it. For critical applications you can look up the various factors and apply them, but for most cases there are simple safe guide lines.

Check the boiler spec, if it is no more than 3A then no problems!
I’m thinking the flex is 0.75mm anyway as 0.5mm seems a bit small
 
The two concepts are
1) how much current is the appliance drawing in normal use
2) in fault conditions will the fuse blow before the flex melts or the appliance becomes damaged.

0.5mm flex is rated for 3 amps. Your current fuse is 5 amps. So irrespective of the load (the boiler) that isn't great as the fuse doesn't protect the flex.

As main priority I'd stick a 3 amp fuse in.
1amp fuse inside the boiler, so I’m guessing it will never be more than that? But what about because it’s on with the upstairs sockets? Which is fed by 32amp MCb. The fuse will protect anything after the it doesn’t it? So as long as my boiler doesn’t drag more than 5amps or 3amps as the case should be, I’m fine?
 
1amp fuse inside the boiler, so I’m guessing it will never be more than that?
Maybe, but not your problem! In any case the fuse should protect the flex to cover highly unlikely circumstances like it getting sliced/drilled through.
But what about because it’s on with the upstairs sockets? Which is fed by 32amp MCb. The fuse will protect anything after the it doesn’t it?
As the overcurrent protective device for the circuit is larger, the supply to the spur isn't really relevant. It meets the regs. The job of the spur is to "fuse down" and protect the smaller flex.
So as long as my boiler doesn’t drag more than 5amps or 3amps as the case should be, I’m fine?
Yes. Being honest I wouldn't lose lots of sleep about how it is right now, but to comply you should stick a 3A fuse in really.
 

Reply to Boiler fuse/cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Wiring cooker hood into a switched fuse spur with a 13amp fuse in the spur. The cooker hood is 3amp. Should I swap out the 13amp fuse in the spur...
Replies
2
Views
327
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
460
The new Advance Combi Boiler has a feed from consumer unit using 6mm cable on a 32amp breaker to a 45amp double pole switch. What size cable to...
Replies
9
Views
1K
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
873
Can I supply my central heating (programmer, two port valves and boiler) via a fused spur taken from the immersion heater circuit? They’re...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock