Jabbajaws

Hi All,

My friend is having his house rewired and ive noticed that the gas meter and main water supply are adjacent to each other.

My question is (under the regs) do they have to have their own bonding conductors or can they be cross bonded, sharing the same bonding conductor back to the MET?

Thanks JJ... :yinyang:
 
By continuous do you mean without being terminated at all?

Ive seen this done before, where the outer insulation has been removed with no break in the conductor. Is that what you mean. Andrew?
 
correct. the idea is that if wet-pants comes along and disconnects 1 bond, the other bond will stilll be intact.
 
A good idea, however The tails are 25mm sq and im sure the regs say that 10mm sq bonding has to be used for main equipotential bonding. Can you crimp 10mm bonding?
 
google non-insulated crimp tool. for the bigger sizes, hydraulic tools are used, but you can get hand crimp tools up to 50mm , no problem.
 
If you get a good earth clamp you should be able to strip a section the sleeving and rap it around the first earth clamp and then terminate it at the second
 
as murdoch said. it's not a reg. it's just best practice.
 
if they are in the same place, or even close i always use one continuous 10mm. much to the annoyance of an old electrician i work with who would install 2 even it it were a 20m run round the house in conduit and the gas and water were within 2 foot of each other, likes using up cable i think!
 

Reply to Bonding question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
1K
Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
Replies
1
Views
314
Hi I have a 1st fix domestic install on the go and need to leave a socket for other trades to use after me. There is no main bonding at the...
Replies
7
Views
831
Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
607
Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
Replies
6
Views
747

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock