And nothing is impossible given the correct circumstances.
Discuss Builder needing advice after damaging temporary supply to new build! in the UK Electrical Forum area at ElectriciansForums.net
Your scenario seems highly likely. The OP really needs a technical report stating the cause and effect of what occurred then I suspect the charges maybe reassessed.Of course where I wrote CNE conductor above, it might be a PEN, but as it caused such far reaching effects it seems not to have lots of decent ground paths shunting it.
Yes the site temp was presumably on TT, but if the service cable was connected to a PME system, an L-CNE fault current could have blown a defective PEN O/C elsewhere, where other properties were relying on it.The only way to ensure safety would be to use a local earth for all CPCs
but the cable was damaged, he should have at least tested the sheathThat's exactly what I thought Richard, sounds like they are trying to blame me for a fault in there network! The engineer got a shock when he touched the outer sheathing wires as he took his gloves off, he obviously wasn't expecting them to be live!
i was on a large steading job, diggers outside working on the underground heating system, then a loud bang and some smoke coming from their ditchHi - apologies if this has already been said or is rubbish (please correct me) - if the DNO cable was concentric, then our man has exposed the N by nicking the cable. The N would have to already have been well above a few volts to cause the bubbly water that's reported. So either more than a nick or distribution system already in trouble, or both (?). A pic of the damaged cable might be interesting .
(please correct me) - if the DNO cable was concentric, then our man has exposed the N by nicking the cable. The N would have to already have been well above a few volts to cause the bubbly water that's reported. So either more than a nick
DNO’s do not connect meters, they will run the service cable to a cut out which may also be TNCS, MOPs supply and fit the meters.DNO will only install a temporary supply using TT, they insist on having the Earth Rod in place or they won’t connect meters.
DNO’s do not connect meters, they will run the service cable to a cut out which may also be TNCS, MOPs supply and fit the meters.
im surprised how the fault caused 2 t.vs to "blow up"Thanks for all your responses by the way, really appreciate all the advice/info!
The fault on your cable should have caused no detrimental issue to the supply network.Looked at the latest email from the supplier and this is what they said!
"The damaged caused an open circuit neutral fault. Where the cable has been damaged it has caused a surge down the overhead network and we have had to replace the ABC conductor and overhead span to rectify this."
"Had there been a fault on the network already we would have known as we would have received prior call outs."
if i was you, id hire a solicitor as it sounds like the 2 neighbours are taking the michael, and so are the supply company.blew up one of their kettles as well apparently!
yeah but this sounds like it was the cable before the service headdon't the DNO fit fuses to prevent such damage to their precious network?
if their fuse didnt react then their system design is a failure, so they should be liable for their own overheads, then the labourer responsible for the damaged cable from overhead to temporarysubstation has fuses as well.
100k? pop that down to the scrappy at lunchtime and go 50/50 with the boss aye?Alasdair's explanation is even more convincing - that it was a PME service that had already lost its neutral upstream and carried on without symptoms. The DNO will have a job arguing that your service cable fault directly caused that problem without at the same time revealing that they were not complying with the ESQCR. Subject to the specifics in the report, I can't see how you could be held responsible for it, or the consequential damage.
FWIW I 've fixed a ton of electronic gear that has been blown up by a wandering neutral. It's a specific hazard in my industry with lots of temporary 3-phase TNS on single-pole connectors and cables. Unlike lightning, which can destroy every semiconductor in one hit, the modest over-voltage of 400V maximum only normally affects the PSU and often just a few components within it. Repair was usually viable and well worth doing, although we sometimes had to write things off for insurance reasons depending on the circumstances. That was professional kit though, where a rack might be worth £100k or more.
Why the dumb Rigpig at least have the decency to correct me or give the other viewpoint.It is where the neutral and earth of the consumer's installation is joined together so on the supply side you have the live conductor and the outer armouring in the combined neutral/earth conductor.
Chances are it's accidental on a phone. I've done it a few times, even when just trying to scroll down the screenWhy the dumb Rigpig at least have the decency to correct me or give the other viewpoint.
Yeah every time i post something loads of people accidentally hit disagree or dislike, really annoyingChances are it's accidental on a phone. I've done it a few times, even when just trying to scroll down the screen
i have a block of granite, i need it turned into dust, how much?RESULT!!!!
The company backed down today and are now only charging for the damage we did to the supply cable! They didn't admit fault of course but said they are dropping all the overhead cable charges!
Can I say a big thanks to all you guys who obviously know your stuff as we used your technical explanations in our replies to the company which I'm sure made them think twice about taking it further!!
Thanks again and if anyone needs building advice I'm happy to return the favour!
could just drive down to trumps golf course and start digging up the greens with a putter, maybe now they are mates he will just fire them at meKim Jong-Un might be able to help you on that one! He has a few nukes he needs to get rid of now!!
i have a block of granite, i need it turned into dust, how much?
5x5x5metres
no idea how guys managed to drill this stuff out before electric motors!We used to get similar problems when it would not fragment with a blast.
View attachment 42752
Stock photo but we used to get them like this regular.
no idea how guys managed to drill this stuff out before electric motors!
think id go mad with the cold chisel and twist method
seen a video of a pensioner on youtube splitting huge boulders with just a cold chisel and bolsterAmazing really when you think of what the ancients done with it.
We got close to a village and had to restrict the amount of blasting and as bad luck would have it we hit limestone . The blasting would only split it. We had Caterpillar D9 dozers in with with single ripper pics fitted ; they hardly looked at it.
I worked with an old stone mason that could do that . He worked at a famous quarry in Northumberland .seen a video of a pensioner on youtube splitting huge boulders with just a cold chisel and bolster
seen guys struggle to drill through concrete slabs without splitting it! they just cant resist using hammer mode even though its soft like butter to just drill through
does amaze me how civilizations with no heavy transport could move such stones
heres the vid of the old bloke
when i was really young i threw a big metal spike straight into the chuckies below me, ended up with a stone stuck in my throat for ages LOL , just think of all the man hours it must have taken to cobble all the roads of britain at one timeI worked with an old stone mason that could do that . He worked at a famous quarry in Northumberland .
He used to hue the winstone from the solid and hand cut the sets for the old cobbled streets . He was amazing to watch.
Isn't that what they used to do to pass time before they invented smart phones?think of all the man hours it must have taken to cobble all the roads of britain at one time
the romans didnt get to cobble much of the roads here, if only the romans knew about north sea oil, i doubt they would have built the wallIsn't that what they used to do to pass time before they invented smart phones?
Reply to Builder needing advice after damaging temporary supply to new build! in the UK Electrical Forum area at ElectriciansForums.net