Search for tools and product advice,

Discuss buried boxes in the UK Electrical Forum area at ElectriciansForums.net

wrighty

-
Arms
Reaction score
7
evening all,

im after a few pointers, could somebody suggest a decent box that can be buried under ground, im looking to install some bollard type fittings in the back garden on top of flags. im thinking of SWA in and out, flex up through flag into bollard.





cheers
 
Personally I would fit a 20mm y box in the bollard. Don't like the idea of a flex buried and then passing through a flag stone.
 
I did type a lovely reply, but the forum did it's usual trick of timing out on me, so I'm not typing it all again...
One word..Hi-tuff

I'd agree, Hi-tuff is good for this application if unlikely to be mechanically damaged. I'd try to get all the terminations above ground if at all possible, even if that means choosing a different bollard light.
 
Why not try a swa through joint buried with flex out one side as well through a conduit up to the fitting? I did this on a job when we had about 15 led up lighters per circuit to light up a tree. :-/
 
Here's a job I did recently using swa glanded into 20mm trouser boxes
ImageUploadedByTapatalk1376778137.313184.jpg

Then bollard bolted on top
 
Pratley boxes are designed for underground use and seem to work quite well (though expensive), but I agree with others, keep joints above ground if possible.
Pratley box EF3Way-400.jpg
I too have not heard them called trouser boxes, but certainly from that picture it looks appropriate.
 
Most of our street lighting is jointed underground, and is not an issue, Good quality jointing kit using potting compound will outlast the swa.
 
Now, if only you'd protected the sheathing from the sharp edges of the concrete, I'd have been really impressed... ;)

Lol I had filed the edges with a rasp which made them smooth lol I suppose I could have used some conduit to protect the cable further lol

all the customer was worried about was that I had set the slabs correctly facing north lol I had my compass out and everything lol
 
Always called 'em trouser boxes.sometims heard then referred to as " 2in, 1 out".
 

Reply to buried boxes in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
733
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
699
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
607
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock