Discuss Buried SWA cable fault finding in the UK Electrical Forum area at ElectriciansForums.net

Quick further thought - if recently installed it will be metal boxes both ends. To ask an obvious question, are you sure the live isn't simply resting on the box the end you aren't testing, with the SWA still glanded to the case and providing the continuity you are seeing? If so this might be a red herring.
I'd be looking first and foremost where the cable leaves the house and enters the garage - are there any joint boxes there that have water ingress.
Obviously if you completely removed the SWA, including glands both ends then this isn't a valid thought.
 
Quick further thought - if recently installed it will be metal boxes both ends. To ask an obvious question, are you sure the live isn't simply resting on the box the end you aren't testing, with the SWA still glanded to the case and providing the continuity you are seeing? If so this might be a red herring.
I'd be looking first and foremost where the cable leaves the house and enters the garage - are there any joint boxes there that have water ingress.
Obviously if you completely removed the SWA, including glands both ends then this isn't a valid thought.
Absolutely, you have got to completely rule out all the obvious and exposed parts first, else it could end up an unnecessary expensive repair.
 
What were all the readings between cores and between cores and armour?
and end to end continuity of each core?

as it’s a 3 core, you could swap the colours and use the shorting out core as earth.

That’s only possible if only one core is damaged. And it’s not a long term solution as any moisture will eventually rot the armour away.
Thanks! Swapping cores isn't something I thought about. I believe my earth and neutral are in good condition so that might work!

Edit: I haven't checked continuity end to end as the multimeter won't reach the far. I can try connecting the other ends and doubling back though. I haven't tried resistance yet but will do asap.
 
Even if you work out how far from each end it is, and unless you know for sure it’s in a straight line and not wiggling all over the place…. You might still end up digging a 6ft wide hole looking for it.

Advise getting a professional with proper test equipment to check it. Your multimeter may not be picking up slight damage to a second core which would scupper my suggestion above.

multimeters give out roughly 9v…. Professional gear- up to 1000v
Thanks mate, I'll look about for a professional but a brief search last night didn't pick anything up. I know the exact root and depth of the cable.
 
Thanks! Swapping cores isn't something I thought about. I believe my earth and neutral are in good condition so that might work!
As my further post said…. Get the cable checked by a professional with the right test equipment. There may be further damage to the cable that you’re multimeter isn’t detecting.

Make sure you identify the cables properly at each end… not just a little flag of tape that could fall off.
Might surprise a future electrician finding a brown core on the earth bar
 
Thanks! Swapping cores isn't something I thought about. I believe my earth and neutral are in good condition so that might work!

Edit: I haven't checked continuity end to end as the multimeter won't reach the far. I can try connecting the other ends and doubling back though. I haven't tried resistance yet but will do asap.

You definitely need to IR test the cable and see what the damage is. The other cores may be damaged also.
 
Thanks everyone.

It's a long story, but in regards to the ducting, these builders were absolutely ripping the arse out of it on day rate. In the end I got so frustrated I just had to settle with a number of things I wasn't happy with including the lack of ducting.

In regards to a second hand Megger I'll look in to that if I can't find an electrician smart enough to do it.

Out of curiosity though, how would an insulation resistance test work and would it help me locate the break? Or just confirm the damage exists?

Thanks again little spark, swapping the cores isn't ideal and a repair was my favoured option but swapping cores might be a good temporary fix!
 
Thanks everyone.

It's a long story, but in regards to the ducting, these builders were absolutely ripping the arse out of it on day rate. In the end I got so frustrated I just had to settle with a number of things I wasn't happy with including the lack of ducting.

In regards to a second hand Megger I'll look in to that if I can't find an electrician smart enough to do it.

Out of curiosity though, how would an insulation resistance test work and would it help me locate the break? Or just confirm the damage exists?

Thanks again little spark, swapping the cores isn't ideal and a repair was my favoured option but swapping cores might be a good temporary fix!

I'd be getting the builders back and getting some of the original bill refunded. . The repair to this cable is going to cost you money - it will almost certainly need an electrician.
 

Reply to Buried SWA cable fault finding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
596
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
850
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
353

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock