Discuss Buried SWA cable fault finding in the UK Electrical Forum area at ElectriciansForums.net

That leaves half of a pair of simultaneous equations and I gave up and opened the 1664 at that point. I’ll return to this one day…
To answer my own question in case anyone searches the forum for varley loop test in future…
The 2nd equation is derived from twice the resistance of a length of one conductor being equal R+X+y. Substituting that in leaves a ratio of resistance X to resistance of the total loop. I think.
I might try this and @pc1966 method out when I have time just for fun.
 
danielz000 - I am no more than 20 minutes drive from you. Do you want me to call in? If the method my colleagues have explained does not work on the damaged 25m length I will improvise a time domain reflectometer and use it during a second visit.

If he was my brother he would have been given an Essex smack for not waiting for some testing to be done ;-)

We will pass circa 50 Amps through the cable in order to produce a volt drop of the order 50 x rho = 50 x 0.00183 Ohm/A/m = 50 x 0.002 = 0.1 V per m or 25 x 0.1 = 2.5V over the length of the 25m cable. May even use an even larger current briefly.

Shall I buy the necessary items or do you want me to guide you through what you need and how to do it yourself? For safety's sake is the house end of the cable removed from the CU so that you would not be working near anything live?
 
danielz000 - I am no more than 20 minutes drive from you. Do you want me to call in? If the method my colleagues have explained does not work on the damaged 25m length I will improvise a time domain reflectometer and use it during a second visit.

If he was my brother he would have been given an Essex smack for not waiting for some testing to be done ;-)

We will pass circa 50 Amps through the cable in order to produce a volt drop of the order 50 x rho = 50 x 0.00183 Ohm/A/m = 50 x 0.002 = 0.1 V per m or 25 x 0.1 = 2.5V over the length of the 25m cable. May even use an even larger current briefly.

Shall I buy the necessary items or do you want me to guide you through what you need and how to do it yourself? For safety's sake is the house end of the cable removed from the CU so that you would not be working near anything live?

The usual knowledge and helpfulness from Marconi, mixed in with a slight hint of violence ?

Be interested to see how this works out.
 
To answer my own question in case anyone searches the forum for varley loop test in future…
The 2nd equation is derived from twice the resistance of a length of one conductor being equal R+X+y. Substituting that in leaves a ratio of resistance X to resistance of the total loop. I think.
I might try this and @pc1966 method out when I have time just for fun.
My concerns with the Varley Loop / Murry loop sort of tests here is the need for high current / low resistance adjustments. With ~25m of 16mm copper the total resistance of each conductor is of the order of 0.03ohms and you will struggle to find rheostats of that sort of value and ~10A rating just sitting around.

My approach is really a "Wheatstone Bridge" arrangement but instead of using the other arms to null (zero) a galvanometer, today we just use a decent DMM that will be > 1M impedance so can be ignored and if 1mV resolution for the meter we can get a meaningful reading / distance resolution with only a 100mV or so total volt drop. The balancing arm ratio then becomes maths on the two measured voltages.

So then test currents of the order of 5A are feasible and sustainable without worrying too much about how to get that much current (mid-size laboratory PSU, car battery with some current-limiting load like a 60W bulb, etc).
 
3. LAP AC/DC Digital Multimeter 600V - https://www.NoLinkingToThis/p/lap-ac-dc-digital-multimeter-600v/161fg that's the multimeter I got but when I tried to measure resistance across the live and armour it just read "ERR". Nothing in the manual about how or why that can happen...
The Screwfix site lacks detailed specifications, such as the voltage ranges/resolutions supported. At least it is CAT-II rated, but that is not quite enough if measuring at the CU (instead of at the appliance after 13A fuse, etc) See:

The usual reason for getting an error when attempting to measure resistance is it is seeing some residual voltage there. It could be the fault is intermittent so only manifesting at higher test voltages so it is picking up capacitively coupled voltages, or it could be there is a small AC voltage of the order of 0.1V or so induced from some other energised circuit or current flowing back via earthed metalwork in the garage, etc.

As general advice, always check for voltage before you measure for resistance! Multimeters are not considered safe for "proving dead" as there are so many ways you can get it wrong, possibly resulting in a fatal shock if you failed to detect high voltages, or an inadequately rated meter exploding if subject to a very high energy fault.

That is what the likes of GS38 health & safety advice call for the use of a dedicated voltage tester, along with some means of proving it is working before and after you checked for the presence of high voltages. This is the sort of thing you would be looking at for a low budget:
https://www.NoLinkingToThis/p/lap-ms8922b-ac-dc-2-pole-voltage-tester-with-rcd-400v/669hy
The proving units are significantly more expensive (in the £70++ range) but for occasional use you can check it works on a circuit you did not switch off before/after you test one you plan on working on.
 
@danielz000 if marconi is offering to come and help, I would jump at the chance. His Knowledge is vast. You may not understand a 100% of what he is explaining to you though ?.

Ps.. I love @Lucien Nunes explanation of why a standard resistance test from each end may well not work! (i.e pin hole and filling channel tunnel). Really helps you see the problem, especially when you cannot understand all of the physics involved.
 

Reply to Buried SWA cable fault finding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
599
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
858
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
353

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock