I have been following a couple of threads 13634-regs-rcbo-s by wire the world and 13628-rcd-testing by king.
A job came in today to do a PIR on a property that I worked at some years ago and I’d like your opinions.
The cutout is in a basement garage, feeding a cu which is high up in the ground floor wc above.
If I remember the cutout position correctly that would make the tails about 3.5m – am I right in thinking that anything over 2m requires a Switchfuse?
Unless I am lucky and the tails are up the cavity, they won’t be buried deeper than 50mm.
30mA RCD in the garage is impractical so I guess its chop out for steel conduit or SWA unless anyone else has any bright ideas?
 
Anyone know where the reg is for meter tail lenght. never come accross it in the book thats all. I know its 3m max but just wondered if somone could point out the number for me

thanks
 
Thanks guys, never found it in the regs either.

I think it may vary with DNO's as I'm sure an EDF guy told me 2m....

Just found in the OSG - the distributor may specify the maximum length - so I guess its an hour on the phone tomorrow!
 
stlightly on a tanjent here but i put a 4inch core hole in once for a fan and cut straight into the main tails which were in the cavity, confusing as the CU was around the front of the house and the meter on the wall behind me. loudest bang i have either heard, the spark was impressive too
 
was better than when i was an apprentice and was trusted to put the busbar in the CU, half asleep and put itin in one continues length through the neutral too, blew a 100A push in fuse on a frday evening at 5pm. that was loud and bright too!
 

Reply to Buried Tails in the Australia area at ElectriciansForums.net

Similar Threads

Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
3K
Evening all.. I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the...
Replies
75
Views
8K
Guest77
G
just after a bit of advice on buried meter tails, the situation is this is a ground floor flat which as had a fire and needs new lighting circuit...
Replies
7
Views
2K
Hi Just looking for some advice on meter tails in a flat. The setup is 5 flats, i originally wired the meter tails in double insualted singles...
Replies
25
Views
5K
I am going to do a CU change for part of my scheme provider assessment, so I want to get this right. Currently the old CU (Wylex bs3036 rewirable...
Replies
26
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock