Search the forum,

Discuss C2 Vs C3 for no RCD on various circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

n180

-
Reaction score
23
So I'm getting various responses to this depending on how things are interpreted.

Here's a scenario:

Assume property is a tenanted property.

Assume cables are run buried in walls/under plaster (depth unknown).

Which of these circuits merit a C2 if they are not RCD protected.

1. Lights
2. Hob/oven
3. Smokes
4. Circuits with accessories/fittings in a bathroom.
5. Socket circuits with no access to outdoor use.
 
Which of these circuits merit a C2 if they are not RCD protected.

1. Lights
2. Hob/oven
3. Smokes
4. Circuits with accessories/fittings in a bathroom.
5. Socket circuits with no access to outdoor use.
Take a look at the Best Practice Guide #4 (free online) as it has useful coverage on most things, but in general my interpretation is:

C1 = immediate danger to life (e.g. exposed live parts, incoming polarity wrong)
C2 = danger if single fault occurs (e.g. no RCD outdoors, as cable cut while gardening and contact with Earth likely)
C3 = improvement recommended (as unusual or multiple fault scenarios present danger that current regs mitigate)

In your list #4 is a clear danger, especially as the supplementary bonding which would have been done to meet previous regs is not always present or maintained over time as plumbers do stuff, etc.

While not in the guidance I think many folks would also be less forgiving of deficiencies in rented property as (a) the owner is making money off it, and (b) the owner is not personally exposed to the risks if they decide not to upgrade.

Finally, the BPG#4, etc, are guidance and you as the inspector has to look at the actual situation to decide how serious the risks are. You can imagine situations where multiple C3s make for an overall unsatisfactory situation, or something like lack of RCD on indoor sockets are a C2 danger based on how you see the occupants using them, etc. For your own protection take photos if you can, and notes of what you saw that merited your decision in case it is queried later.
 
Technically all are C3. Overall satisfactory outcome. Make sure all are listed under the observations though.

However, being a rented property, the landlord should be encouraged to make things as safe as possible.
Strongly worded footnote, highly recommend upgrade to consumer unit…etc etc

Send a quote to upgrade in with the report.
 
This is the whole 'RETROSPECTIVE' thingy...

IF the circuits were all installed and have remained completely untouched prior to the 17th Ed then it can deemed they meet the Regs of that Era and Code 3 will suffice. You can not Code 2 somethings retrospectively as it was deemed compliant at the time of installation.

However if you have any way of reaching an extension lead from a socket Via a window or back door then I would be inclined to C2 it anyway
 
You can not Code 2 somethings retrospectively as it was deemed compliant at the time of installation.

Yes you can, if it is now considered potentially dangerous then it is a C2 regardless of when it was installed.

There is nothing in the regulations to say that you cannot code something a C2 if it complied at the time of installation.
 
That's true, however in most cases what you can see of the cable is less than 50mm depth.

What I'm asking I guess is, all the circuits 1 to 5 I mentioned above, can in general constitute c3 because it met previous regs, however what if:

A. You know or can see it's less than 50mm or
B. You don't know the depth, is a LIM on the depth enough to justify a c3 or would an rcd now be a requirement?
 
can in general constitute c3 because it met previous regs
Forget whether it complied with previous Regulations or not. It really has no relevance as to its safety given our current (excuse the pun) understanding of this. Instead just consider it on the basis of what safety deficit a non-compliance poses, and how serious that is.
 
can in general constitute c3 because it met previous regs, however what if:

No, it is C3 because it is not a potential danger, it is something which could be improved for safety. It is additional protection only.

B. You don't know the depth, is a LIM on the depth enough to justify a c3 or would an rcd now be a requirement?
If you have an agreed limitation to the inspection then that is something that you do not inspect or test, you don't give it any 'C' code, you just record LIM against that item to indicate that it was a limitation on the inspection.




If an RCD is required for additional protection but is not fitted then it will generally be a C3, the protection it gives is additional to the primary protection.

If the RCD requirement is not for additional protection but is as a part of the primary form of protection (fault protection for example) then it would be a C2 for it not being fitted.
 
Presumable no SPD, plastic CU, so another couple C3’s there.

If there’s no bonding, then it didn’t comply in the first place, so that would be a C2. Can’t have EEBADS without the EEB.

Everything can be solved by replacing the board to all RCBO of course, so a cover letter with the report, a quote as mentioned by me earlier, and hope they think it’s a job that must be done.
 
C2 = danger if single fault occurs (e.g. no RCD outdoors, as cable cut while gardening and contact with Earth likely)
Hey, can you explain to me how the gardening example is different to no RCD protection inside a property? Is it just the contact with the physical earth which is different?

Thinking on that, how can we actually get a belt if we're standing on wood inside our home, since we're not in contact with earth/are only in contact with something that is an insulator?
 
Hey, can you explain to me how the gardening example is different to no RCD protection inside a property? Is it just the contact with the physical earth which is different?

Thinking on that, how can we actually get a belt if we're standing on wood inside our home, since we're not in contact with earth/are only in contact with something that is an insulator?
Because you are standing directly on the ground which is also possible wet. As you say less likely to get a larger shock standing on your wooden floor in your house. Also your more likely to cut through a cable with the hedge strimmer than a hairdryer 😀
 
If your body is completely isolated from any means of return then you shouldn't receive a shock. I used to stupidly demonstrate this to apprentices by happily touching live parts.
What were you standing on when you did this lol? I've seen all the vids of people doing this but even if i knew i was insulated i wouldn't have the balls to do it.
 
I never really took any precautions made a snap decision and did it. Stupid thing to do and did it countless times and experience told me i was kinda 'safe'.
 
Because you are standing directly on the ground which is also possible wet. As you say less likely to get a larger shock standing on your wooden floor in your house. Also your more likely to cut through a cable with the hedge strimmer than a hairdryer 😀
More likely to drop a hairdryer into a sink full of water though….
 
I never really took any precautions made a snap decision and did it. Stupid thing to do and did it countless times and experience told me i was kinda 'safe'.
So was this just standing inside a property?

It's also interesting that people seem to get shocked and killed by appliances in the bath even though they're typically upstairs, in an acrylic tub, which is bolted to wooden flooring, and is part of a building only in contact with the earth via bricks. You'd think you'd be fully insulated.
 
So was this just standing inside a property?

It's also interesting that people seem to get shocked and killed by appliances in the bath even though they're typically upstairs, in an acrylic tub, which is bolted to wooden flooring, and is part of a building only in contact with the earth via bricks. You'd think you'd be fully insulated.

You become part of the circuit and a wet human body has very low resistance, allowing current to flow though it - perhaps even more easily than through the water surrounding you.
 
Best example I can think of is birds sitting on power lines are in contact with live electricity and suffer no ill effects.

If a larger bird makes contact with a second line or something in contact with earth, they get fried as they have now formed a closed circuit.
 
It's also interesting that people seem to get shocked and killed by appliances in the bath even though they're typically upstairs, in an acrylic tub, which is bolted to wooden flooring, and is part of a building only in contact with the earth via bricks. You'd think you'd be fully insulated.
In a bath you are frequently connected to the Earth via the service pipes. Modern installations with all-plastic pipes might save you as the pure water in the pipes is not very conductive, but given it only takes a little over 30mA to induce heart fibrillation if you are unlucky, you only need under 7k ohm to be killed which can be reached with wet dirty wooden floor boards, etc.

The bathroom is typically the most vulnerable location due to folks being wet in there and many are small so any appliances like heated towel rails, etc are often within arm's reach of the bath/shower, etc. Not to mention the electric showed being in there!

In the 1970s and early 80s (I think) you used to get public information 'adverts' on TV warning about the dangers of electric shock in the garden as most houses lacked RCD protection, but folks were now moving to electric mowers and hedge trimmers instead of doing it by hand. Every year there you could read of a half-dozen or so folks killed by slicing a cable / extension lead and the tool being live and them on the grass, etc.

So there was a campaign to get folks to use RCD adaptors, etc on extension leads or to fit RCD sockets. Over time most houses would be rewired or at least have a CU upgrade so by early 2000s it was becoming less of an issue but you will still find properties lacking RCDs and for specific locations (e.g. outdoors, bathroom) the risk of an accident and/or the vulnerability of the person to the results are much higher than your typical indoor case.

Of course now with battery tools being affordable, convenient and quite powerful there is less need for mains outdoors, but its still a real risk.
 

Reply to C2 Vs C3 for no RCD on various circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all, we got an EICR report done before tenanting our previous home having become "accidental landlords". See attached. The report came back...
Replies
12
Views
4K
I have recently had an EICR on my tenanted 1st floor purpose-built flat, built in 1995. I have received C2 codes for lack of RCD as follows: 5.14...
Replies
16
Views
2K
Hello, I've recently had an EICR done on my 2 bed house which is a residential let. This house is about 25 years old built by Charles Church...
Replies
86
Views
27K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock