Discuss Cable Calculations on Ring Circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
11
Hello,

I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get lost when it comes to ring circuits.

If I take my Ib and In as being 32A for example how would I go about selecting a cable size and proving it is acceptable for the Iz? I know rings are typically wired in 2.5MM but installed in refence method B for example that would only be 23A is there a formula to show that the multiple paths of the ring allow for the cable to carry more or do I just need to state this.

Thanks for your help.
 
The RFC is a special case, that has been proven by 75 years of use to be safe and reliable. The intended application is for general distributed loads spread randomly around the circuit, leading to reasonable sharing between the cables. If the load is spread evenly along the length of the ring, it will be shared equally and the highest current the cable needs to handle is In/2 = 16A. I am not near my regs but could someone please confirm (with reg no. if poss) that any cable with an installed Iz of 20A is permitted? This allows for the load to be somewhat unevenly distributed, e.g. if a large appliance is near one end, or one leg of the home run is longer than the other, resulting in up to 20A in one leg and 12A in the other.

In theory you can contrive a situation where In or Ib > Iz and the cable is technically overloaded. E.g. put four fanheaters at the first few sockets on one leg and nothing anywhere else. However the overload will be modest and these situations are rare and usually of short duration. A cable that will withstand Iz for say 50 years, might have its life reduced a few percent this way, but seeing as no-one is going to run the ring at 32A non-stop for 50 years, let alone have four fanheaters at one end for the entire time, the cable will probably outlast its spec anyway.
 
Last edited:
Thank you, couldn't remember whether it actually stated Iz>=20A or just the CSA. For no obvious reason, the regs were sat on the piano for months, but now I actually want to look something up at home they're in the office. Because for many years I've only really been involved with machinery / theatre / studio technical installations, it's a very long time, decades probably, since I actually installed a ring.

Also, welcome to the forum, @iDragonBox. Stick around, there is lots of knowledge available here, along with good banter / humour / nonsense.
 
Last edited:
Thank you, couldn't remember whether it actually stated Iz>=20A or just the CSA. For no obvious reason, the regs were sat on the piano for months, but now I actually want to look something up at home they're in the office. Because for many years I've only really been involved with machinery / theatre / studio technical installations, it's a very long time, decades probably, since I actually installed a ring.

Also, welcome to the forum, @iDragonBox. Stick around, there is lots of knowledge available here, along with good banter / humour / nonsense.
Thanks a lot for the information was looking in my regs book trying to find something and looking for the reg online to no avail! Really helped me out so thanks a lot.
 

Reply to Cable Calculations on Ring Circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
430
Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
2K
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
417
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
324
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
953

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock