Discuss Cable choice for a 10.5kW Shower in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

L

Lofty

Hi All,
Looking to fit a 10.5kW shower for a builder and he is virtually insistant that we use 16mm T&E as 'That's what he has been told to use in the past'.
The installation is in a bungalow so the run will be in the loft where I can clip it direct above the insulation. The run is about 15mtrs max from CU to shower and we think that 10mm T&E would be OK with a 50A MCB etc.
So 16mm or 10mm

Cheers Lofty,
 
16mmm my a**e. how can you terminate that in a shower isolator. 10mm is bad enough. 10mm on 50AMCB is fine.
 
ask your builder if he can hump 1cwt. blocks of concrete up a ladder as his normal bricks are too small for building chimneys
 
Hi telectrix & Malcom ,
Exactly our thoughts as well. 10mm can be a b**ch to terminate anyway.
Will have to tread carefully with this guy as he is a new builder working for an established customer so don't want rock the boat.

Thanks again for the confirmation, and the speedy replies
 
6mmm would suffice,47A clipped direct, up to 20metres, unless they've changed the rules again.
 
Last edited:
The installation method is very important here, as the CCC for 10mm T&E varies form 64A method C to 32A method 103.

If it is clipped direct and not touching any insulation the a 10mm will suffice.
 
The installation method is very important here, as the CCC for 10mm T&E varies form 64A method C to 32A method 103.

If it is clipped direct and not touching any insulation the a 10mm will suffice.

totally agree just left a post on another shower question ,have a look at page 31 table 2.3.1 installation referance methods , although we can only designe for when the installation is done , we do have to be sensible especially with all the insulation thats being installed around the country and they are putting in 6" ontop of whats there they do not go under the cables but over them so if you look at cable installation method 103 as lenny has said then 6mm is rated at 23.5 amps 10mm at 32 amps and 16 mm at 42.5 amps so the builder is quite correct if the installation method is 103
 

Reply to Cable choice for a 10.5kW Shower in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the...
Replies
18
Views
2K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
483
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
522
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock