Discuss Cable Current Carrying Capacities. in the UK Electrical Forum area at ElectriciansForums.net

nivag

-
Reaction score
3
I'm wiring a corn dryer up and the supply is into an isolator rated at 100a 3P N and Earth then straight into 6mm and 2.5 stranded singles going off in various directions to different MCBs, contractors etc
No fuse down between cable sizes. However this is uk new production. Adding up the various MCB ratings inside the control panel (not allowing any diversity) exceeds 125A

Surely this is wrong?
 
need more info.are these various MCBs 3 phase or are some single phase? the actual load current may be far less than the rated values of the MCBs.
 
Correct me if I'm wrong. But I thought any cable must be capable of carrying the maximum current of the supplying upstream overload device.
Also once the dryer is under full load surely the 100a isolator is undersized.

Thanks for your reply
 
Hi Nivag - the addition of mcb ratings may exceed the isolating switch rating but the current drawn shall not. So the real question is what current will the dryer take? On the cable size changes I don't do it. Why put in 6mm at all if 2.5 is sufficient. The cct must still be mcb for the 2.5 and in future some poor sod might make the mistake of thinking the whole lot was 6mm ... Cheers, David.
 
Hi, thanks for the response, the last bit of your post didn't make much sense to be honest. Maybe it's how I'm reading it.

I understand that the maximum current will be on startup and will drop dramatically once running. I will get it all finished and use temporary 25mm tails to supply it from the genny, the. Clamp meter it and see what it's pulling before I order the supply cable. I'd guess a 16mm 5c sy flex will suffice.

On the cable sizing issue, if it was me wiring it, I'd supply it via, say, 16mm to the isolator, load side in 16mm to a 3p buzzbar then MCB it there before any cable size drop.
I think what I'll do is trace the wires to see what there actually supplying and considering its situation, the fact that I'm just connecting up to it, and it shouldnt be accessed anyone else then, So long as the 2.5 feeds, for example, the 2g 13a metal clad socket mounted to the side of the enclosure, then I know the 2.5 should never exceed 26a
 

Reply to Cable Current Carrying Capacities. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
875
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
Hi Guys Any one know the current carrying capacity of a 4mm 3 core single phase sy cable ran in a 20mm pvc conduit? Not sure of the right table...
Replies
2
Views
933
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
I have a 37KW motor and need to replace some burnt out 35mm2 tri rated cable(loose connection). I’ve looked at 25mm2 Tri rated cable the data...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock