Just wondered how other people handle running cable horizontally ie between 13 amp outlets, where there are load of batons for taking the Plaster Board on a Stone/Brick wall.
Especially on thin Batons, Yes RCD Protected as NOT 50mm depth.

Thanks
 
horizontally between accessories is safe zone, so ok.
 
One way is to make smallish holes in the plasterboard over each of the batons. Notch the baton, run the cable and plaster over the holes.
 
I would try and go vertical espicially if there is a good distance between the sockets. IMO running cables horizontal is ok in a kitchen type enviroment if you have sockets, FCU, double pole switchews virtually next to each other, Most people would not expect horizontal runs if there was say 2 meters between the sockets.

I know it's classed as a safe zone, but so is running cables 150mm horizontal along the ceiling line or 150 vertical between the V of 2 wall, for me it don't sit right.

The only other thing I can think of is, are you going to weaken anything by cutting or drilling through a lot of batons. I would personally try and go vertical.
 
if you,ve got access above under floor, then , yes , it is better practice to loop over ceiling and vertical drops to sockets.

Hate to admit it, but malcolm is right
 
Last edited:
I often use the 'padsaw out a little bit then notch the batten' approach as described above. Also, you could have a look at getting one of those freeform drill bits - they are long, semi flexible bits which you can use to drill in tight environments, then tie your cable to the end of the bit and pull it through, cable rod style. I'm thinking of getting a set myself.
 
I often use the 'padsaw out a little bit then notch the batten' approach as described above. Also, you could have a look at getting one of those freeform drill bits - they are long, semi flexible bits which you can use to drill in tight environments, then tie your cable to the end of the bit and pull it through, cable rod style. I'm thinking of getting a set myself.

Thanks will have a look at the flexible bits as not seen them yet. If it helps the padsaw work that would be great ( hate padsawing) and will have to do some of it no doubt.

Any links to the Flexibile bits
 
Thanks will have a look at the flexible bits as not seen them yet. If it helps the padsaw work that would be great ( hate padsawing) and will have to do some of it no doubt.

Any links to the Flexibile bits
rocker only uses padsaw and drill bits if he can't find his hammer . LOL
 

Reply to Cables behind a Baton and Plaster Board wall in the Australia area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
918
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi Guys & Girls, It's been a while, hope everything is good. I have an issue that's proving to be a bit of a head scratcher. Please bear with...
Replies
11
Views
2K
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
Hi Ive been asked to fit some lights and a socket in a new stable yet to be built but its giving me a bit of a head ache. I haven't done a stable...
Replies
44
Views
4K
44ALLAN
4

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock