I’m an Industrial electrician and as such have limited knowledge of domestic installations (we all still use the same regs though). I’m wanting to know what people do about the increased insulation in lofts.

For example my shower is a nominal 9.5kW with a 10mm T&E cable If I was to install the recommended 250mm of insulation the cable would no longer be the right size As even though the cable would be lifted out of the insulation, 250mm goes through to the switch, back out and then to the shower so as much as 750mm would be in the insulation (clipped to the beams).

What do you guys do about this ? I was thinking of putting some sort of wooden boxing to keep the insulation about 100mm away from the cable.

Thanks for any advise.
 
just move the bloodyitchy snot out of the way. it' may save a shilling on the gas bill but is a major contributor to damp/mould/ decay. a house needs to breathe.
 
I would like to see you try terminating a bigger size cable.? Move the horrible stuff out of the way, clip the cable up on the joists if not boarded.
 
By moving it out the way I assume you mean I should cut it so it's kept away from the cables when it's installed. The loft will be boarded that's why I was thinking of using a piece of wood to make sure the insulation doesn't spread/move across to the cable.
 
do what ever. as long as the cable has a decent air space around it. think of farting in bed. if the covers are tight, your missus will get a hefty niff. loose covers, it just floats away to create more global warming.
 
if you are DIYing it and got some spare time then make kind of channels/trunking for the cabling, free of insulation, with separate openings from the top, will make it easier for future maintenance or additions, no need for lifting whole boards and looking where the cables may be.
 
Easy enough to keep above the insulation, and where it goes through it, use a piece of plastic waste pipe.
Yes, you could build a little box around it for retro-fit, or cut a slot out of said waste pipe.
 

Reply to Cables in loft Insulation in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
756
Hi Everyone, Sorry for all the questions. With he help of a friend, I recently installed some insulation into my mother's loft. Whilst adding...
Replies
3
Views
1K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
726
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
160

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock