arkboy105

DIY
Reaction score
0
I recently rewired my laundry room with MC cable, 20 amp circuit. I installed an AFCI/GFCI combo switch. The gas dryer trips it as soon as I plug it in, under no load. The washer does not trip it. I tested it with other appliances, under high load, no issue. This doesn't seem like a nuisance tripping to me, since the dryer isn't even running when it trips. Is this an indication the wiring in the dryer cable is bad? No issues before but it was only on a GFCI.
 
I recently rewired my laundry room with MC cable, 20 amp circuit. I installed an AFCI/GFCI combo switch. The gas dryer trips it as soon as I plug it in, under no load. The washer does not trip it. I tested it with other appliances, under high load, no issue. This doesn't seem like a nuisance tripping to me, since the dryer isn't even running when it trips. Is this an indication the wiring in the dryer cable is bad? No issues before but it was only on a GFCI.
You are correct that it is not a nuisance tripping issue. If it was working on a GFCI circuit then why change it. By code you protect all laundry room it is required to be by a GFCI breaker or receptacle not AFCI protection. Since it’s gas operated it could be detecting the igniter or seloniod. Hope this helps and welcome to the forum.
 

Reply to CAFCI/GFCI tripping immediately when plugging in dryer in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

I have a towel dryer on an interior wall in my bathroom, wired off the last stop in my loop of bathroom outlets. This thing has been installed...
Replies
10
Views
931
I have a small power washer with a two-wire cord and GFCI plug. My outdoor and garage receptacles are on a "house GFCI" circuit, wired in series...
Replies
2
Views
2K
Hi, We’re having problems with our Bosch serie 6 washer/dryer. It’s about 6 years old. The model number is WVG30461GB/03. It has begun to stop...
Replies
0
Views
510
Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
512
GFCI green light is lit when not under power draw. The bidet seat functioning causes light to pulse yellow (and creates a pulsing and knocking...
Replies
1
Views
338

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock