Discuss calculation for maximum demand in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Ok, diversity is as follows:

Lighting - 66% of total current demand for each circuit
Power - 100% of the first ring circuit + 40% of all other circuits
Cooker - First 10A + 30% of remaing rated current + 5A if the CCU has a socket outlet
Shower - No diversity allowable
Instantaneous water heater - 100% of largest heater + 100% of second largest + 25% of of any others
Thermostatically controlled water heater - No diversity allowable
Underfloor heating - No diversity allowable
 
I'm sure you know, but for less experienced people browsing this forum, those examples are for domestic i.e, a house. There are two other types of premises, basically shops+offices, and hotels+B+B's etc.

Just noticed that you are asking about maximum DEMAND, not just diversity, will have to wait for someone more intelligent ;-)
 
Last edited by a moderator:
on site guide page 96 although seeing how im just a boy and i wanted to research this, what is the calculation all well and good saying 66%. but say i went to a job:
cooker x 32
shower x 32
2 x rings x 32
immersionx 16
2 x lights x 6
smokes x 6
from here what do i do and calculate ? much appericiated.
 
right scrap my last post :) but if say you have a 60a with loads of stuff on to much is being drawn what will be the worst outcome ? regards
 
Or take the largest rated mcb and add 40% of the remaing breakers total rating will give you a realistic value for domestic purposes
 
Hi peter, my first thread this after watching for a while. Doubt you'll read this, its so long ago and bet you've got there by now.
As i understand it maximum demand is just the sum total of the CB's supplying the circuits of an installation. eg if our consumer unit had a 32A, 20A and a 16A CB, the max demand would be 68A.

Diversity being the allowances we apply to the circuits to give a more realistic value of how much current we would expect each circuit to carry under normal operation. This is put very well by Lenny above. Do like ezzzekiel's method though, its much simpler, will create some numbers and see how well the 40% rule compares to Lennys.
 
you really need to give careful consideration when calculating maximum demand and diversity, as if you go too strictly on bs7671 guideline amounts then you will end up with huge a demand when in reality the total load will never reach anywhere near that amount, you also must consider the likely use for the installation too, there is not a formulae that will be accurate for every eventuality, for example an upstairs 32a ring circuit in a domestic property will likely never see close to 20A for any period of time let alone 32A!, but in a big kitchen it is more likely to be higher and for a longer duration, adding up mcb ratings will just end up with silly figures, you have to assess the installation and use your experience, things to look for in a domestic property are generally kitchen ring mains, electric showers, immersion tanks, electric cookers and electric heating, things like smoke detectors i wouldnt personally even consider.
 
Last edited by a moderator:

Reply to calculation for maximum demand in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

How are you calculating maximum demand for the certificate and what should you do if your calculations exceed the main fuse rating?
Replies
9
Views
654
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
791
Hi as per title I'm building a sublimation heat press. i have a 1000mm x 250mm x 8mm sheet of cast aluminium. i will be using a thermostatically...
Replies
1
Views
338
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Im currently in my apprenticeship and completing an assignment that involves cable calculations. Im currently stuck on how to find the design...
Replies
1
Views
594

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock