Discuss Can connection plate be replaced by plug socket in the UK Electrical Forum area at ElectriciansForums.net

qPaxxx

-
Reaction score
1
Hi,

I’ve been living in a “new built” house for the last five years and the time to replace some of the built-in appliances has come.

My dishwasher and washing mashine are connected to the grid via connection plates similar to those, although I’m not aware of their exact technical parameters -

12099B60-9F0F-4EB9-A353-98ABB24C9640.png


The wires from those connection plates then go into something like this kitchen multi gang switch -

0CE5C54F-44E9-47E5-860B-DB42CBAE85BD.png


My question is if it would be a good idea, in terms of safety mainly, to replace the connection plates with plug sockets? The connection plate from the link has a 25A fuse, while plug sockets come with 13A. Would this be a problem?

If replacement is possible, would it be better to use one with or without switch?

I haven’t checked the oven, but I assume the same approach has been adopted there. Is the above replacement applicable there too?

P.S. The connection plates are located behind the appliances, which are under kitchen top, but not directly under the sink.
 
Why do you want to do this? It’s fine as it is.


Other thoughts:
25A fuse??? Is that in the consumer unit?

As above. Show us a photo of the actual kitchen grid switch.

Personally, I hate sockets being located behind appliances. Think what happens if a fuse blows that powers a washing machine. Those things are heavy enough, but the fuse will go leaving you to pull out a washing machine plus a full load of wet washing and a gallon or three of water.
 
The grid switch has fuses (13A for dishwasher, haven’t checked the oven) and switches
2880DCF8-29B1-4EB4-A646-E0BFA995EBC0.jpeg


The idea behind replacing connection plates with plug sockets is not to have to cut the plug of the new appliance in order to connect it to the grid, as my understanding is that this will void the warranty.

Also any future replacements might happen a bit more easy in theory.

I think there would be enough space to fit a plug socket and potentially a one that is IP66.

The 25A comes from my Internet searches. The connection plate pictured in my previous post is a 25A one - Deta 25A 1 Gang Connection Plate. I don’t know if my current ones are 25A, but my Internet searches show that most connection plates are 20A or 25A. I suggest that any new appliance that I buy would be fused at the plug at 13A?
 
Agreed. It will not void the warranty.
If you introduce a fused plug onto the cable, you will then have two 13A fuses in series:
One in the plug and one in the grid switch. That is BAD design. You should not have two fuses of the same value protecting the same device. You should have a higher value at the supply end and a smaller one protecting the load. The only way you could achieve that is to strap out the fuse in the grid switch. But that is a totally pointless exercise!!’
It’s all find as it is. New appliance, chop the plug off and hard wire it in as it is now.

Don’t get confused about the 25A reference. That is NOT a fuse of any sort. The 25A is just the maximum current that the item can handle before it melts.

Similarly, leave the oven as it is.

In fact, leave everything as it is. Put a chair in the garden, pour yourself a beer, read the paper. That would be a better use of your time.
 
Wish I’d kept a link on here to my research about cutting off moulded plug (tops ☺️).

@qPaxxx as chaps have said, cutting off manufacturers moulded plugs should not void any warranty. However, from my research there are some manufacturers who think it does.

I recall when stipulating that if their supply lead and or plug was damaged, only a replacement lead from them should be used. Their lead plugged into the appliance.

Not many but worth double checking.
 
Thank you very much for your advice.

I will adhere to it and not undertake any changes. I’ve spoken to AO customer service and they assured me the guarantee will be void, but nevertheless I prefer it void than introducing dodgy practices in my house (in terms of electricity of course:))

Thank you very much again:)

Edit:
Actually are there any un-fused plug sockets that can replace the connection plate? Or this would BAD idea as well?
 
Last edited:

Reply to Can connection plate be replaced by plug socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
403
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
976
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
641
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock