Discuss Can I spur a socket from an existing fused spur on a ring main? in the DIY Electrical Advice area at ElectriciansForums.net

coliander

DIY
Reaction score
0
I'm sure this has been asked before, but I just want to confirm:

Currently I have a spur leaving a socket in the bedroom, into a 13A Switched FCU and running up to power a double socket in the loft.
I now want to locate a socket in the old boiler cupboard/airing cupboard to power a tumble dryer (relatively low load heat pump unit).
The simplest way to do this would be to place a junction box in the loft and between the FCU and the loft double socket and run power back down to the socket the boiler cupboard.
Is this permissible/safe? And should I place another FCU before the boiler cupboard socket, or will the existing FCU on the loft feed be sufficient?

Ta.
 
TL;DR
If I run a spur from an existing spur, do I also need a seperate FCU for the new spur?
If the spur is fused, then you can have more than one point after the fuse. Any load past the fuse would be limited by the 13A fuse.

Does the airing cupboard not already have a supply to it for a boiler or old immersion? These are likely to be on a 16A radial, and can be reused to run a socket.
 
  • Like
Reactions: DPG
Thanks for the quick response.

Around a decade ago, the old warm air heating system was upgraded to a central heating/combi boiler setup and it appears that the supply to the cupboard was decommissioned at the same time. When I purchased the property, the original fuse box had an allocated space for the old boiler fuse, but it was vacant. The only wiring remaining was from the room thermostat back to the cupboard.
Pity, because that would have made things a lot cleaner!
 
Thanks for the quick response.

Around a decade ago, the old warm air heating system was upgraded to a central heating/combi boiler setup and it appears that the supply to the cupboard was decommissioned at the same time. When I purchased the property, the original fuse box had an allocated space for the old boiler fuse, but it was vacant. The only wiring remaining was from the room thermostat back to the cupboard.
Pity, because that would have made things a lot cleaner!
Is it Rcd protected ?
 

Reply to Can I spur a socket from an existing fused spur on a ring main? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
651
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
394
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
665
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock