Hi Guys,
Looking at a motor problem today. Nothing big, just interesting.
An SP 400 watt motor with, it appears capacitor start phase shift. Press the start and the motor hums and gets warm but doesn't spin. Having tested all the lives with a MM I removed the capacitor. If I flick the cooling fan the motor runs. Suspecting a dead start cap' I discharged it and tested with an ohm meter - an open circuit either way round. Suggests the Cap' was OK so what have I missed?
20180505_123637.jpg 20180505_123657.jpg 20180505_123859.jpg
 
Hi Guys,
Looking at a motor problem today. Nothing big, just interesting.
An SP 400 watt motor with, it appears capacitor start phase shift. Press the start and the motor hums and gets warm but doesn't spin. Having tested all the lives with a MM I removed the capacitor. If I flick the cooling fan the motor runs. Suspecting a dead start cap' I discharged it and tested with an ohm meter - an open circuit either way round. Suggests the Cap' was OK so what have I missed?
View attachment 42086 View attachment 42087 View attachment 42088
Could be a fault with the centrifugal switch on the motor shaft which switches the start capacitor out of circuit, at about 75% full speed.
 
TBH it's not professional kit with a plate; just tile cutter I was investigating out of curiosity. Seeing the little dial on the back of the stop/start I wondered if the start cap' was on a timer?
 
TBH it's not professional kit with a plate; just tile cutter I was investigating out of curiosity. Seeing the little dial on the back of the stop/start I wondered if the start cap' was on a timer?
Most cases the start cap will be centrifugal switch controlled but without a picture it's nye on impossible to tell
 
.........I discharged it and tested with an ohm meter - an open circuit either way round. Suggests the Cap' was OK so what have I missed?
Usually you'd get a brief reading on an ohmeter whilst the cap partially charged then when you reverse the probes you'll get a bigger 'kick' or reading whilst it discharges which will diminish as it recharges again.

As mentioned above use a capacitance tester to test it properly or just replace it anyway because they're cheap
 

Reply to Capaciter Start Motor converted to flick-of-the-finger-start query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
687
Would you consider a single phase Shower Pump Motor operating with a temperature high enough to burn finger tips touching the motor body, to be...
Replies
4
Views
1K
I picked up a 7.5W 110V TEFC single-phase induction motor for super cheap. I may use it on a home made lathe or stationary-sander for my woodshop...
Replies
7
Views
2K
Hi Sparkies, newbie here needing some advice please My 1100W SDS hammer drill sometimes starts, sometimes dead. So far fault diagnosis (loose...
Replies
11
Views
2K
I'm looking at a German made roller conveyor system 10 motors contactors controlled by a PLC Issue is customer says 3 mths ago motors started...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock