What allowance for diversity, if any, would you apply to caravan hookup sockets?

The circuit will have just one hookup point, with two 16A sockets. It's a fair distance from the CU, so voltage drop is going to be significant. It would be good to keep the cable CSA down if feasible.
 
I'm in the design stages/site preparation of something similar, but for four points.
Each point has a 16 interlocked, switched socket protected by a 10A type C RCBO, and I've allowed 24A as the design current.
The only long term heavy load likely to be drawn by a touring caravan is the electric space heating, which is usually 2kW max.
 
New posts

Reply to Caravan diversity question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

There’s been a few recent threads about caravans, caravan sites etc, and I thought I’d post up some photos I took today while on one such site...
Replies
0
Views
900
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
767
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock