Small private building site. I'll be setting up the temporary supply soon.

TT then small RCD garage unit inside the meter box on a post (DNO agrees that OK), and couple of IP66 sockets under. All good.
But customer also has a titchy site caravan alongside. - Sect 708 calls for INDIVIDUAL 2-pole RCD for each caravan supply. This complicates an otherwise neat little job.

Bearing in mind main RCD in CU is 2 pole, and demand limited to a computer and kettle, might you go for 13A plug to BS EN 60309-2 adaptor (about £5) for the caravan cable? (For a rather minor BS7671 infringement)?
 
i'd fit a 2nd RCD for the caravan. tin hat on. OK, you then have no discrimination between the RCDs, but that's an inconvenience, n ot a safety issue. IMO, safety overrides convenience.
 
Are you reading the rules for touring caravan pitches and then applying them to a fixed caravan by any chance?

Unless people are coming to visit this building site for their holidays that is.
 
when OP said a titchy caravan, i assumed a small tourer. metal skinned. i stand by my previous post.
 
Yes ordinary caravan. As you say Telectrix, no actual "harm" in loosing discrimination. It's all temporary and everyone will know what they are doing. So maybe just fit standard caravan outlet. Ta for the thoughts.
 
Where do you get them from? I've never yet seen a DP RCBO in single module format, only SPSN
Compact RCBO Mini RCBO Circuit Breakers
www.electricalcomponentsdirect.co.uk/.../Compact_Mini_RCBO_Circuit_B...
ECD Compact RCBO 2 pole B curve 6A 1E-2PB6 RCBO 30mA 2 POLE 1 MODULE WIDE SAME SIZE AS A MCB Compact Mini RCBO Circuit Breakers are new ...

[PDF]SINGLE MODULE DOUBLE POLE RCBO - Proteus Switchgear
www.proteusswitchgear.co.uk/downloads/sp rcbo dimensions.pdf
Page 1. SINGLE MODULE DOUBLE POLE RCBO DIMENSIONS. SWITCHGEAR. ' 1—. 6.80. 50.30. 66.80. L.
 
The ECD ones in your first link have no spec sheet or wiring diagram with them so impossible to tell for sure but they look like SPSN and the description suggests that ether than DP

And looking through the whole proteus catalogue I can't see any DP RCBOs, only SPSN ones
 
Small private building site. I'll be setting up the temporary supply soon.

TT then small RCD garage unit inside the meter box on a post (DNO agrees that OK), and couple of IP66 sockets under. All good.
But customer also has a titchy site caravan alongside. - Sect 708 calls for INDIVIDUAL 2-pole RCD for each caravan supply. This complicates an otherwise neat little job.

Bearing in mind main RCD in CU is 2 pole, and demand limited to a computer and kettle, might you go for 13A plug to BS EN 60309-2 adaptor (about £5) for the caravan cable? (For a rather minor BS7671 infringement)?
Buy a dual rcd caravan socket from denmans which is a inclosure with 2 sockets on it and 2 double pole 32 amp rcds and mcbs inside it, you can change the mcbs for 16 amp if you like and the whole unit is no more than 60 quid.
 

Attachments

  • mqkT6GllS8a6hJkhRA68zFw.jpg
    6.8 KB · Views: 38
The ECD ones in your first link have no spec sheet or wiring diagram with them so impossible to tell for sure but they look like SPSN and the description suggests that ether than DP

And looking through the whole proteus catalogue I can't see any DP RCBOs, only SPSN ones
Garo 16 Amp 30mA 1 Module RCBO Type B - Meteor Electrical
Garo 16 Amp 30mA 1 Module RCBO Type B| MeteorElectrical.com
Garo 16 amp 30mA double pole single module RCBO. Double pole; Rating:16 amp; Sensitivity:30mA; Trip type:B; Test button for periodic testing; BS EN 61009 ...
 
The ECD ones in your first link have no spec sheet or wiring diagram with them so impossible to tell for sure but they look like SPSN and the description suggests that ether than DP

And looking through the whole proteus catalogue I can't see any DP RCBOs, only SPSN ones

now go and wash your mouth out with carbolic.
 
Proteus 6 out of 10 ive used them a few times im in agreement with tel about RCD's but you could always put in a time delayed one up front
 
OK. Ideas here. I just want to keep it all compact and squeeze the CU into the top corner of the meter box. Hence 4 unit wide garage module is about as big as I want too go.

Q) 708.553.1.13:
I assume caravan site socket outlets are to be DPRCD protected individually, mostly for convenience reasons and to isolate faults to individual caravans. Necessary on a commercial site.

Inconvenience would be irrelevant on this small site. On that basis, if I had a garage unit DP RCD feeding site sockets (32A MCB) AND a single BS EN 60309-2 caravan socket (16A MCB) then the caravan socket is "individually" protected - because there are no other caravan sockets.

Disregarding convenience, is there any actual safety reason why this would be a bad idea?
 

Reply to Carvan supply, small building site in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, New job looking at. I haven’t been to site yet, but this is the scenario. DNO just put a new single phase supply into a field PME...
Replies
5
Views
1K
hi all i was just in the middle of doing an eicr on a caravan park and wanted some opinions on what codes are relevant to the site. ive got tncs...
Replies
32
Views
7K
P
Hi Guys I'm doing an EICR and making expansion proposals for a Caravan Site. This is for holiday not static caravans. Simple question - how many...
Replies
7
Views
7K
Piratepete
P
A
Hiya all What we have is a holiday home site type effort where there are 13 caravan type looking units of accommodation. They do not have towing...
Replies
15
Views
3K
E
Hi All, I've got a job to do at new caravan site. The client is paying for 3phase off of the pole that runs through the field and they have...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock