Discuss Category for lack of RCD on sockets in 27 year old building in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Hi Russell you can get free down loads from electrical safety first look at guidance document 4.
If the sockets can be used for outside power ie lawn mowers and the like it's c2 if not c3 . It's upto the enginer on the day as long as they can justify the code.
Thank you Flyman, that was my understanding. Not much chance of using the sockets for outdoor purposes on the 2nd & 3rd floor, unless of course they use a hover mower LOL.
 
according to the regs/.nothing to do with any code breakers or other irrelevant publications, it's clear as a bell.

immediate danger e.g exposed live parts).......C1

potiential danger, e.g. danger present if some other action compromised safety, ........ C2

no appearent danger, but not compliant with current regs. ........ C3.

what's the problem?
Thank you for your corroboration. That is exactly what I thought and can back it up with the regs and guidance note three but a seed of doubt was planted as I am not familiar with this publication EICR Codebreakers. However the book has just arrived and I am going to have a read.
 
Basically BPG#4 suggests C2 for outdoor or wet area electrics lacking RCD, C3 for other cases. Of course it is more about domestic inspection.

If you are in a commercial/industrial location with a good policy/application of PAT testing/inspection of any equipment used in the sockets being considered then I would see it hard to justify anything but C3. Excluding outdoor or wet areas obviously!
 
As a side note I watched a long vid on codebreakers (the people part of making it) and their justification very much related to domestic rented premises. As tenants could be very variable and their equipemnt so it is sensibly arguable in those circumstances that (maybe) C2 is justified. I think error could creep in where people are following advice which is not statutory or regulations, and take that as the same authority, it is very important to distinguish what guidance one follows. Personally I am very circumspect as regards following non statutory/regs advice.
 

Reply to Category for lack of RCD on sockets in 27 year old building in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
989
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
767
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock