Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been wired in old red, L2 old Yellow, L3 old blue, however as stuff has been added it's now got new colours. The property is currently empty awaiting new tenants, I've been in today to start an EICR and have already come across 240v between Neutral to earth on 2 of the L3 circuits.
Coding the neutral/live polarity issue obviously but just looking for other people's thoughts on coding the old colours for a lack of identification in regards to live colour? I would always sleeve a black cable with brown if used on a single phase circuit is why I'm thinking this way...
Then I think I'm being over the top but clearly a previous electrician has got neutral and Live mixed up with the blue cable.
thoughts please
Coding the neutral/live polarity issue obviously but just looking for other people's thoughts on coding the old colours for a lack of identification in regards to live colour? I would always sleeve a black cable with brown if used on a single phase circuit is why I'm thinking this way...
Then I think I'm being over the top but clearly a previous electrician has got neutral and Live mixed up with the blue cable.
thoughts please