Discuss 3 phase motor running backwards wire colours in the UK Electrical Forum area at ElectriciansForums.net

will_505

DIY
Reaction score
1
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as I'm not sure.
Cables I've got are: brown, blue, black and green/yellow.
I've currently got brown wired into live 1, blue into live 2, black into live 3 and green/yellow into the neutral/ earth pin. Just to clarify its only a 4 pin plug I have. I have a suspicion the motor is running backwards as the compressor just doesn't sound right at all. Have I wired this plug up correctly?
Any help is appreciated cheers.
 
Last edited:
The positive phase sequence is L1 Brown, L2 Black and L3 Gray. Is the blue colour you mentioned actually gray?

See:

https://www.tlc-direct.co.uk/Technical/DataSheets/Cable/CableColoursLeaflet.pdf

post a picture of the plug Connections. The thickest pin is for the earth not neutral so you connect green/yellow to it.

Study this carefully:

Industrial Extension Leads ltd - https://www.industrialextensionleads.co.uk/plug--connector-types-explained-4-w.asp

The positive phase sequence is L1 Brown, L2 Black and L3 Gray. Is the blue colour you mentioned actually gray?

See:

https://www.tlc-direct.co.uk/Technical/DataSheets/Cable/CableColoursLeaflet.pdf

post a picture of the plug Connections. The thickest pin is for the earth not neutral so you connect green/yellow to it.

Study this carefully:

Industrial Extension Leads ltd - https://www.industrialextensionleads.co.uk/plug--connector-types-explained-4-w.asp
Please see photos attached of the wires I have in the plug. It's entirely possible I've gotten it wrong. Or I may be colourblind!
 

Attachments

  • Snapchat-1615807119.jpg
    229.4 KB · Views: 25
The cable in use clearly as you said has a blue conductor which is being used as a the L3 phase conductor - normally identified by gray colour.

I take at face value you have tidied up the exposed copper connections.

It would be best if you could mark up the blue conductor to identify it as L3, by applying gray sleeving, brown sleeving with L3 written on it or any tape folded over it with L3 written on it.

Does compressor now function?
 
The cable in use clearly as you said has a blue conductor which is being used as a the L3 phase conductor - normally identified by gray colour.

I take at face value you have tidied up the exposed copper connections.

It would be best if you could mark up the blue conductor to identify it as L3, by applying gray sleeving, brown sleeving with L3 written on it or any tape folded over it with L3 written on it.

Does compressor now function?
Hi yes I did tidy it all up I just put it together to show how I had it set in the first place. Not with the machine at the moment but, the blue wire in the photo should be in L3, brown should be L1 and black should be L2 correct?
The machine did function the way I had it to start with I was just convinced it was running backwards as didn't sound like any of my other compressors ever have lol..I'm away ATM but I will wire it in the following way: blue: L3, brown: L1, black L2.
Cheers
 
Assuming it is actually running in the wrong direction which may not be the case. There could be an issue with the generator.
 

Reply to 3 phase motor running backwards wire colours in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm trying to wire in a 4 core capacitive sensor into a safety circuit. I have brown, blue, white and black coloured cores and it's a NO sensor...
Replies
1
Views
217
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
334
Hello, disclaimer: this is DIY and I am rather ignorant about electrical works. I just moved into a new rental apartment and i wanted to connect...
Replies
11
Views
514
Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
989
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock