Hi,
Hope someone can help me please
Have six ceiling downlights in my kitchen, recently one of the bulbs stopped working so I replaced it, these lights have a retaining spring clip which stops the bulb from dropping down. My problem is I now have three of the lights not working, have checked the bulbs and checked the wiring all is ok. Is it me in re-fitting the spring clip not correctly? Can the lights just dangle from the ceiling and still work or do they need the clip to act as an earth?
Any info/advice would be greatly appreciated
Many Thanks
Phil
 
even dangling from the fitting, the lights should still work. my guess is that you've disturbed a loose connection thus stopping the 3 lights from working. as they are daisy chaied, a break in either L or N conductor will stop any lights further down the chain from working. if you're not confident to find this, call in a spark. simple job should not take more than an hour.
 
Hi Phil,


The clips have absolutely nothing to do with the functioning of the downlights, they are just there to keep the fittings in place in the ceiling.
I would suggest that in the act of you taking the fitting down a wire has come loose possibly in a joint away from that light and you must be careful when looking for this, proper procedures must be adhered to with regards to isolation etc.
You are probably going to need some professional assistance i'm afraid.
[automerge]1584452002[/automerge]
The clips have absolutely nothing to do with the functioning of the downlights, they are just there to keep the fittings in place in the ceiling. I would suggest that in the act of you taking the fitting down a wire has come loose possibly in a joint away from that light and you must be careful when looking for this, proper procedures must be adhered to with regards to isolation etc. You are probably going to need some professional assistance i'm afraid. Tel in first again lol
 
Turns out it was the transformer a cheap one from B&Q of course they don’t do them anymore so had to buy three new ones with their own transformers and now the holes are slight bigger aargh!!
 
As others have said about disturbing a loose connection over time with the old halogen lamps quite often the wire would have got so hot it disintegrates and just about makes until the lamp fails, then you come along take the lamp out and disturb it and it no longer works.
 
Turns out it was the transformer a cheap one from B&Q of course they don’t do them anymore so had to buy three new ones with their own transformers and now the holes are slight bigger aargh!!
Just replace the transformer not the light fitting. Almost anywhere is cheaper and better than b and q also.
 

Reply to Ceiling Downlights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have an electrician over and he took over from an incompetent builder. The builder already installed the wiring but the electrician told me...
Replies
22
Views
1K
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
700
I have 16 ceiling spots to be replaced in a room being repurposed as a bathroom. Some will be over a shower, basin and bath hence need to be IP65...
Replies
19
Views
1K
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
555
My bedroom light stopped working. The ceiling rose looks fine. No other lights are affected in the property and the fuses have not tripped. The...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock