Discuss Certifying remedial including dist board swap. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
9
Hi,

An easy question if you know the answer.

My house recently failed an eicr done by me.

I've had a couple of jobs I'm fixing (split ring separating into 2 circuits), and some I'm not (no cpc on plastic light switches Upstairs, presumably compliant at time of install. The lights have a cpc as a later addition).

I'm swapping the distboard to full rcbo/metal to give me the room to split the ring to two circuits.

So for the schedule of tests....what needs doing?

Just certify the board/supply?

The above + circuits repaired?

Every connected circuit?

Every connected circuit and two sub dbs with their circuits?

This is going to be notified directly so want to know what should completed?

I'm testing everything, but if I'm completing the full form, then what do I do about the C3?
 
So for me all the circuits should be on the schedule of test results.
No earth at switches is a C2 unless mitigated by warning notices at consumer unit advising only class 2 equipment to be installed at switches
Strictly speaking no class 1 equipment should be installed on circuit & warning notice at CU advising only class 2 equipment to be used
 
So for me all the circuits should be on the schedule of test results.
No earth at switches is a C2 unless mitigated by warning notices at consumer unit advising only class 2 equipment to be installed at switches
Strictly speaking no class 1 equipment should be installed on circuit & warning notice at CU advising only class 2 equipment to be used
I'm under the impression that you didn't used to need a CPC on a lighting circuit?

As it was compliant at time of installation, only a c3 is required as a minimum?

It is the crux of the issue. I only want to certify the dist board, not every circuit in the house.
If I put the lights on the schedule of tests am I certifying compliance with current regs (which it does not meet)?
 
If changing a consumer unit you're certifying the consumer unit.
However, as you've changed the characteristics of every circuit, you also need to test every circuit for continuity of protective conductors at a minimum.
If any circuits would not comply to the extent that a C2 would apply to that circuit, then you must not reconnect that circuit until the C2 has been rectified.
Electrical Safety First has published free guides on how to treat a lighting circuit with no CPC when changing a consumer unit.
 
If changing a consumer unit you're certifying the consumer unit.
However, as you've changed the characteristics of every circuit, you also need to test every circuit for continuity of protective conductors at a minimum.
If any circuits would not comply to the extent that a C2 would apply to that circuit, then you must not reconnect that circuit until the C2 has been rectified.
Electrical Safety First has published free guides on how to treat a lighting circuit with no CPC when changing a consumer unit.
All the answers I needed on that thanks!

Complete test sheet, all non-compliances to be listed under 'condition of install' and circuit notes.
 

Reply to Certifying remedial including dist board swap. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
876
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
934
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Opinions on this Crabtree TP 10 way board? Got to test this next week after a quick recce on a clients site yesterday. Although probably...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock