Update on problem.

After posting first of all I asked a friend who I used to work with to look at it, as he used to wire all the boilers.

He went round and said it was the programmer so changed programmer and still same problem. Went back today to check all wiring and all seems ok. Wiring is as following:

Live, neutral and earth from spur to programer.
Ch on to wiring centre joined to white of 3 port valve.
Hw on to wiring centre from programer joined onto cylinder stat.
Return on cinder stat connected to live to boiler and Orange on 3 port valve.
Satisfied from cylinder stat joined to grey on 3 port valve. The programmer does not have a Hw off that should be joined also with the grey on 3 port valve. This is not a problem as they have the Hw set on all the time.

All the wiring seems to be ok if the above is correct. But the ch does not seem to switch off even with the programmer turned off.

Tested voltage on Hw on only at Orange of 3 port valve and gives 230v if stat is turned down 230v goes away.

At white of valve reading 230v with Hw on and ch off. Disconnected white at programmer and getting 230v still but nothing on cable to programmer meaning voltage coming from valve side. Is this correct for the valve to bring the white live when Hw is on? Or is it possible its back feeding at valve causing ch to come live?

Sorry for the long reply

Thanks
 
It's the 3 port valve then. This is what valves tend to do when they go. I have a question what sort/ make of 2 chanel programmer doesn't havnt a hw off, it would be nice to know so I never fit one. Good luck
 
Hi invisible

The programmer has a hot water off its the wiring that is missing the core from programmer to the 3 port valve connected to grey on valve and satisfied on cylinder stat.

As above when the Hw was on the ch was off it was giving 230v on white on 3 port valve coming from valve side not programmer. So you think it will be the valve faulty?

Thanks
 
Sounds like it.
Can you discconect the valve from the wiring centre (if it wired like that) then just check your cables coming back from the programmer then you could be 100% sure.
As mentioned before in this thread if it was working fine before then it is more than likley it would always be a bit of faulty equipment and it is normally the valves that go, and when they go that is what normally happens.
 
Hi, Been to a job today with exactly the same kind of symptoms. Boiler firing up in the middle of the night when programmer is turned off but the pump is not running so pipes are banging because of heat waking the customer up. Thought it was a problem with frost stat as this is what plumber said to me. This is a s plan system but boiler is in garage, side of boiler is a 15 amp switch and frost stat. Also there is a pipe stat above boiler. Cannot understand why it would have a pipe stat as I thought boiler would have a built in overheat stat and frost stat. When I turned up the pipe stat from 20 c to 40 c the boiler fan fired up ? So basically when pipe stat falls below 20 c it fires up the boiler. Back of frost has a perm live into terminal 3 which should be sw feed back up the yellow in my book? this has confused me all afternoon and hopefully I have now sorted problem by removing the pipe stat. I thought that the pipe stat would be for overheat not call or am i wrong.
Any advice would be great to clear my head up
thanks
 
Hi, Been to a job today with exactly the same kind of symptoms. Boiler firing up in the middle of the night when programmer is turned off but the pump is not running so pipes are banging because of heat waking the customer up. Thought it was a problem with frost stat as this is what plumber said to me. This is a s plan system but boiler is in garage, side of boiler is a 15 amp switch and frost stat. Also there is a pipe stat above boiler. Cannot understand why it would have a pipe stat as I thought boiler would have a built in overheat stat and frost stat. When I turned up the pipe stat from 20 c to 40 c the boiler fan fired up ? So basically when pipe stat falls below 20 c it fires up the boiler. Back of frost has a perm live into terminal 3 which should be sw feed back up the yellow in my book? this has confused me all afternoon and hopefully I have now sorted problem by removing the pipe stat. I thought that the pipe stat would be for overheat not call or am i wrong.
Any advice would be great to clear my head up
thanks



"Hello brooky25",


I am a Heating Engineer - the reason for the Pipe Thermostat being fitted in conjunction with the Frost Thermostat is because the Boiler only needs to Fire occasionally for Short Periods of Time during Cold Temperatures to Stop it from Freezing - the Boiler does NOT need to Fire until the Boiler Thermostat Setting is reached.

The Pipe Thermostat is fitted so that the Boiler only Fires to remove the Immediate `Threat` of Freezing - So it does not need the Boiler to reach a High Temperature such as would be on the Boiler Thermostat Setting.

However from what You described it sounds like it was NOT wired Correctly - it should only be operating in conjunction with the Frost Thermostat - and I am assuming that it was not Cold enough when You were doing this to have caused the Frost Thermostat to be in Operation [?].


I would advise You to refit the Pipe Thermostat as the Combination of a Frost Thermostat and a Pipe Thermostat IS the Correct Method of providing Frost Protection for the Boiler in this instance.


Regards,


Chris
 
Last edited:
Many thanks for the advice Chris, I do believe you are right iv'e been thinking about this all night. I am going to go back and sort the problem. The trouble is new tennants have only been in property 3 weeks and previous tennants have moved to Aus, so I don't know how long the problem has been there or who has messed with it. Need to start from beginning with this as in my head there should be sl,n,e going to boiler from orange on valves to call for heat and perm l,n going to frost stat then sw out of frost stat through pipe stat back to call on boiler. Am I correct ?

P.s Sorry for hijacking this thread
 
Last edited by a moderator:
HONEYWELL FROST THERMOSTAT AND PIPE THERMOSTAT - WIRING GUIDE Capture.JPG
Many thanks for the advice Chris, I do believe you are right iv'e been thinking about this all night. I am going to go back and sort the problem. The trouble is new tennants have only been in property 3 weeks and previous tennants have moved to Aus, so I don't know how long the problem has been there or who has messed with it. Need to start from beginning with this as in my head there should be sl,n,e going to boiler from orange on valves to call for heat and perm l,n going to frost stat then sw out of frost stat through pipe stat back to call on boiler. Am I correct ?

P.s Sorry for hijacking this thread


"Hello brooky25",


Sorry if this is Disappointing - But I will have to `Bow` to Your Electrical Knowledge / Any wiring Diagrams that You can find online / on Here - as I cannot remember How a Frost Thermostat and Pipe Thermostat should be wired.


In the Past My Heating Systems have usually been wired by a Qualified and [about last 6 - 7 Years] Registered Electrician - as it was always required by the Client that ALL Electrical Works were Tested and Certified by an NICEIC Registered Electrician / Electrical Company.


Although I do know how to Wire Up various Heating Systems `S Plan` etc. - the addition of a Frost Thermostat and a Pipe Thermostat would always require Me to be able to read the Wiring Diagram / Wiring Details.

Could I suggest that You go onto the Honeywell website where I am fairly confident that You will be able to find the Wiring Diagram for a Heating System which includes a Frost Thermostat and a Pipe Thermostat - as these Two Stats should always be used in conjunction with each other.


IF You have Time I am sure that some of the Extremely Helpful Electricians / Electrical Engineers on here will be able to perhaps Post a Diagram for these Thermostats to be wired to an `S Plan` System.


Regards,


Chris


EDIT - I have found and Attached a Screenshot from the Honeywell website regarding Frost Protection Thermostats - I hope that it will be Helpful in Identifying the Wires and where they are connected.


Chris
 
Last edited:
Thank you very much for your help Chris, after your explanation of why pipe stats are needed I have found out what the problem is. Thinking back to how its been wired ( altered ), they have wired both stats in parallel not series and I think pipe stat is on flow not return. After a quick search I now fully understand how the system works and how it should be wired. Someone has definatly altered the circuit, most prob plumber. This is what has thrown me. I am a Niceic registered electrician but these heating systems I rarely come across. All will be wired as it should be and I will post the outcome. I always seem to get jobs that others have tried and failed at to rectify. Thanks for helping me get it clear in my head it seems so simple now. (Must have had a blonde moment)
Thanks again
Lesson learnt, Never listen to a plumber who does not know how the system works
 
Last edited by a moderator:
Thank you very much for your help Chris, after your explanation of why pipe stats are needed I have found out what the problem is. Thinking back to how its been wired ( altered ), they have wired both stats in parallel not series and I think pipe stat is on flow not return. After a quick search I now fully understand how the system works and how it should be wired. Someone has definatly altered the circuit, most prob plumber. This is what has thrown me. I am a Niceic registered electrician but these heating systems I rarely come across. All will be wired as it should be and I will post the outcome. I always seem to get jobs that others have tried and failed at to rectify. Thanks for helping me get it clear in my head it seems so simple now. (Must have had a blonde moment)
Thanks again
Lesson learnt, Never listen to a plumber who does not know how the system works



"Hello brooky25",


I Edited My last Post to Attach a Small Wiring Diagram from the Honeywell website - From the Frost Thermostat section - this shows the Wires from the Frost Thermostat and Pipe Thermostat - and where they are connected to in various Wiring Plans.


I expect that you have already worked out what goes where or found a `Full` Wiring Diagram - BUT - Just in case this Helps You or others - I was Pleased to Post it.


Regards,


Chris
 
Yes Chris, Worked it out and your diagram confirms this. Thanks for your time and advice its much appreciated
regards
Mick



"Hello Mick",


Its been a pleasure to be of Help - I realise that it was just the description of why the Pipe Thermostat is required that was of Help - as I would never try to advise an Electrician on Electrical Wiring.


"Thanks" for showing that You appreciated My small amount of `Help`.


Regards,


Chris
 

Reply to CH turning on by itself problem in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
620
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
445
Hi guys, Do you know if I can install a Nest E with the heat link in the airing cupboard as opposed to the room stat position? System is a S plan...
Replies
1
Views
722
Hello I have a central heating system, with a Y plan layout. The neon indicator on the thermostat seems to be sometimes dimly lit / flickering...
Replies
1
Views
773
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock