Discuss Changed a switch, and now there's no power to other rooms. in the UK Electrical Forum area at ElectriciansForums.net

phlip79

DIY
Reaction score
0
I installed a motion sensor switch in our laundry room. It works.

But, now the lights in the next room won't work, and a couple power outlets down the hall don't have power.

Posting a photo of the box. Please let me know what other useful info I can provide?

Thanks in advance.
 

Attachments

  • Screen Shot 2019-11-19 at 10.26.10 PM.png
    910 KB · Views: 42
I installed a motion sensor switch in our laundry room. It works.

But, now the lights in the next room won't work, and a couple power outlets down the hall don't have power.

Posting a photo of the box. Please let me know what other useful info I can provide?

Thanks in advance.
You must have broken the Live feed, or N to the rest of the switches when you installed the Motion Sensor
 
I installed a motion sensor switch in our laundry room. It works.

But, now the lights in the next room won't work, and a couple power outlets down the hall don't have power.

Posting a photo of the box. Please let me know what other useful info I can provide?

Thanks in advance.
Phlip are you sure you hooked the Motion detector right and are the only 2 wires we see that was hooked to the original switch
[automerge]1574281116[/automerge]
Phlip are you sure you hooked the Motion detector right and are the only 2 wires we see that was hooked to the original switch

Phlip you have your 2 black wires crossed
 
ok,
there are 3 wires that are being used, ignoring the grey ones that you have not touched?

one is a permanent supply
one is a feed out to other switches that need a permanent supply
one is a feed out to the light that was fed from the switch.

this is only an educated guess but I suspect that you might have got the connections wrong.
if you joint all 3 wires together then the light should be on and the other circuits should work.
edit,
i have just thought about @Megawatt comment and he is probably correct.
 
I believe the blacks are the hots (live in, live out) and red the traveller (live to light). The blacks look separated now but should be together.
 

Reply to Changed a switch, and now there's no power to other rooms. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

And now for something completely different! I have been after a power station telegraph for decades and due to the fact most would have been...
Replies
7
Views
1K
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
850
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
944
Hi, Need some help with an odd setup. I have a large room with many lights that i separated into 2 sets. In Box 1 there is the 14/2 power in, 2...
Replies
4
Views
1K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
568

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock