Discuss Changing from Halogen to LED in the Lighting Forum area at ElectriciansForums.net

Jim_Lad

DIY
Reaction score
0
Hi,

First time posting on here so apologies if I'm missing any basic information, but hopefully someone can help me as an amateur DIY-er and definitely not electrically knowledgeable. I suspect the best approach would be to get in a professional to help, which I'll likely do but interested in having an idea before getting someone in. I can do basic wiring but obviously would prefer safety / abiding the electrical law over saving money.

Info:
  • House built in 2004, just purchased and finding all the fun expensive 'projects' to do.
  • Trying to convert spotlight halogen to LED's but read about checking the transformer, this lead me to check behind all the lights and they seem to have varying items wired in before the bulb fitting.
  • As on the PDF one appears to have burning on the cable and has gone hard, not sure if this an electrical failing or it's just been resting on the hot bulb - either way I'm pretty sure this isn't safe.
  • Document shows what bulbs are currently in each location along with the type of transformer.
  • Detail of the items shown in each room can be read on the larger images bottom right.
  • Ignore blue and brown lines, they just inform me of the orientation based on the door / window.

Questions:

Apologies if the information is covered elsewhere but I think I have some specific oddities!

Thanks in advance for any advice.

Jim
 
TL;DR
What to do with existing transformers to change from halogen bulbs to LED.

Attachments

  • House Electrics v1.pdf
    1.5 MB · Views: 16
My advice, take out all the halogens. Fire risk if not installed correctly.

also, change them all to 230v GU10 LED replaceable lamps or sealed fittings. the transformers can heat up themselves if covered with insulation, never mind the heat from the lamps.

some disagree about sealed fittings as you need to replace entire unit when fails, and not always possible to get exact match after a few years. It’s just cheaper to replace lamps when needed.
Don’t be tempted to get cheap lamps or fittings from eBay or aliexpress. Buy from reputable sources

The GU10 lamps can usually fit in the same fitting as the G5.3 12v, you just need to change the lampholder.

check the wiring.
The earth wire should be continuous through the circuit, even if it’s not used at a fitting, it still needs to be present.
Any joints to the fitting need to be inside an enclosure. Either part of the fitting itself or separate. Choc block connectors wrapped in tape does not constitute an enclosure.
 
best solution is to remove all transformers, then wire 230V direct into either:

1. GU10 LED bulbs fitted inexisting cans, or:

2. Integrated fittings similar to those in your post.

If going for option #2, check the hole size in the ceilings, easier life if new fittings are same cut-out size. most common is 70mm.
 
just to add. isolate circuit at CU before starting, or even turn main switch off.
 
Not sure its as straightforward as just changing the lampholder to GU10, as most 230v GU10 fittings I've ever used require an earth connection as Class 1, therefore converting from 12v to 230v on a Class 1 or non double insulated fitting may need an earth connection unless of course using double insulated GU10 lampholders.
 
As above. Rip out all the transformers. Hopefully there’ll be enough slack to cut out the crispy cable. Install 230v fire rated integral or GU10’s.
 
Thanks everyone for the quick and informative replies, also appreciate the safety advice ?.

Holes are 65mm (of course they're non-standard!) so look like they would need enlarging - thanks for the advice to check.

Regarding the actual electrics, this has answered a lot of questions but as usual raised a few more- sorry! If anyone can help further it would be appreciated.

  • In at least one circuit there is the brown circle object with cables coming in and out, and then a transformer (see image attached). Does anyone know what this is for and should it be removed if fitting the new lampholders? Looks like there's some kind of earth cable inside maybe?
  • Do I need different downlights in a room that gets damp (i.e. either or all toilet, bathroom, shower)?
  • Regarding the note to check the wiring, does this mean just visually or is there a device to actually check all safe?
  • I assume not from looking online but is double insulated the same as fire rated? I can't see many double insulated options if anyone has any examples please. I've found some but...

This doesn't look double insulated - Fire Rated Cast GU10 Downlight Chrome - https://www.toolstation.com/fire-rated-cast-gu10-downlight/p32910#full-desc
This looks like these might be what I need for all rooms including ones for the shower? I was hoping for some cheaper ones from a standard DIY store - Double Insulated Recesed Downlights | Class 2 | Lightahome.net - https://www.lightahome.net/double-insulated-recessed-downlights-39-c.asp

  • If doing this I'll obviously hope the cable before the transformer is long enough to get to the lamp, if not can I just extend with a short bit of wire and an encased junction box or is this a no no?
  • Can I legally do this work myself? (though if I have further questions after any responses to the the above it may indicate someone qualified would be the best option!)

Thanks again for the information, really appreciated!

Jim
 

Attachments

  • In Line Feature.jpg
    247.8 KB · Views: 12
Ok... the brown thing is a joint box... older type. The top screws off, and there's 4 terminals inside.
Not really used now as there's no cable grip. (unless the box is screwed down, and the cables are clipped going into it.)
 
The Tool Station fitting is Class 1 and the earth conductor can be seen clearly at top of the picture.

The Lightahome fittings are Class 2 (Does not require earthing), however the circuit wiring earth wire (cpc) is sleeved with green/yellow need to be connected throughout to ensure good continuity but only a test with a meter will properly confirm that.

Double insulated is NOT the same as fire rated
(Class 1 = Singularly Insulated, Class 2 = Double Insulated)
IP 65 recommended for bathroom areas.

65mm was pretty standard for non-fire rated fittings.

The new fittings will accept 2twin and earth cables and you can do the job yourself as no re-wiring involved but if you need to extend any cables a maintenance free junction box is recommended and ensure cpc's are fully sleeved at every termination.

Testing for continuity may be a different proposition though.
 

Reply to Changing from Halogen to LED in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
Hi all, I am trying to replace my halogen wall uplights (230W, 240V, R7S, 114mm) with LED but so far no luck. I've tried both of the below LEDs...
Replies
5
Views
1K
This is the second set which won't work to replace the current spots here in my kitchen. All they do is flash once quickly. I'm replacing...
Replies
3
Views
1K
Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
520

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock