Currently reading:
chasing into concrete screed floors - a risk to the neighbour's lights?

Discuss chasing into concrete screed floors - a risk to the neighbour's lights? in the UK Electrical Forum area at ElectriciansForums.net

L

laike

i live in a 1960s built ex-local authority flat. the floors are concrete with approx 30mm of screed poured on top, brick walls. the existing cabling is all MICC which i'm considering ripping out, not because it doesn't work but because i'm looking to move some walls and chase new central heating pipework into the concrete floors. am pretty certain this is going to nick an MICC cable and the circuit will be screwed. not to mention it's not much more expensive to do a full rewire than to find someone who can repair MICC.

QUESTION:if i'm chasing into the screed to run my new cables, is there a risk that i could cut the neighbour's below me lighting cables? is there a chance their lights are running through my screed? (if not, how did they possibly run their lights to their bedroom as their ceiling / my floor is concrete?)

really frustrating job this, if there are any certified NICEIC sparks reading this who are keen to take it on, get in touch. location: dalston, london.
 
Not had time too read all the above posts,
But my house has a concrete screed floor downstairs. So essentially what you have is everything goes to the first floor void and drops down or goes up.
The central heating was surface mounted in mini trunking. I have chased this into the walls. Then into an inspection box. From here it's buried using plastic pipes wrapped in insulation within conduit. Then another inspection box at each radiator bottom for the legs.
Hope this helps
 
=Engineer54;765902]If a conduit installation, the conduit runs would be within the slab, installed just after the steel re-bar fixers, with the conduits tied to the re-bar. Never seen a conduit installation run on top of the slab, as for anything else, it would be out of it's installations equipotential zone, if located as you state, especially if were talking for a block of flats situation...

]Thats how we do it here and have done since day one, but in the 60's in the UK the steel conduit was laid on the top of the slab, the holes for the lights were formed when the slab was poured and there was a 100mm soft screed laid over the slab which covered the conduits, heating pipes etc, I dont know how they do it now, you may have never seen it but thats the way it was done all over the country and if you could bend the stuff and you could earn a fortune as most sparks were paid per flat for first fix

I'll say it again, i've never seen conduit installed this way, not in all the years i've been in the industry. It makes no sense whatsoever cost wise, or electrically!! I can only think that your talking about precast concrete slabs?? But even then, installing a metallic electrical distribution system that is outside of it's equipotential zone, again makes no sense!! And in the 60's it's unlikely that any CPC's would have been part of the wiring of that conduit system either!!
 
structural engineer comes out to the flat.

'where's the screed?'
'right there'
'have you got a chisel?'
'here'
*chisels a massive chunk out*
'yes that's screed, chase away. can you pay me £540 now?'
 
More to the point, ....what did the Structural Engineer say about your intentions to knock down walls in the apartment?? That's far more important than any screed you have over your slab floors!!! lol!!
 
he said it's fine, but the council surveyor already told me that. was a complete waste of money, basically. i guess if the building does collapse a la that dhaka primark factory at least i've got a letter saying it's not my fault - though i'd probably be crushed in the process.
 
I'll say it again, i've never seen conduit installed this way, not in all the years i've been in the industry. It makes no sense whatsoever cost wise, or electrically!! I can only think that your talking about precast concrete slabs?? But even then, installing a metallic electrical distribution system that is outside of it's equipotential zone, again makes no sense!! And in the 60's it's unlikely that any CPC's would have been part of the wiring of that conduit system either!!

I understand that you may not of seen it and you find it hard to believe, but high rise flats were wired in metalic conduit laid directly to the floor slab which was not pre cast, the lighing for the flat below was installed on the slab of the flat above, we did not install earthing conductors in the conduits as the conduit was the earthing conductor, the earth connection at the lighing point, switch or power outlet was via a cable connected to the earth lug in the box (which we had to install whilst installing the box) a soft sand screed was laid on the slab to produce the floor, this screed covered all of the conduits, I am not a liar or making this up, what I find hard to believe is the fact that you seem to want to argue when I thought the point of the forum was there to help each other, however, enough said, I know what work I carried out and how it was done on many high rise site in London, I hope there are some old buggers like me who carried out the same type of work.
 
I understand that you may not of seen it and you find it hard to believe, but high rise flats were wired in metalic conduit laid directly to the floor slab which was not pre cast, the lighing for the flat below was installed on the slab of the flat above, we did not install earthing conductors in the conduits as the conduit was the earthing conductor, the earth connection at the lighing point, switch or power outlet was via a cable connected to the earth lug in the box (which we had to install whilst installing the box) a soft sand screed was laid on the slab to produce the floor, this screed covered all of the conduits, I am not a liar or making this up, what I find hard to believe is the fact that you seem to want to argue when I thought the point of the forum was there to help each other, however, enough said, I know what work I carried out and how it was done on many high rise site in London, I hope there are some old buggers like me who carried out the same type of work.

I am one of those old buggers, but as i say, only seen conventional methods of installing conduits into slabs. ...lol!!
 
Marty203 are you sure you are not getting mixed up with maisonettes as I could then understand if their downstairs lighting conduits came from their bedrooms above. Perhaps if you where a young lad at the time you may of only worked on those parts of a large job and not remembered or recalled the conduit arrangements for the bedroom lighting which should of been cast into the slab?
 
Many years ago I can remember wiring some brand new flats in the Midlands area. We used Volex pre-wired PVC conduit which was buried in the above flat floor screed. The Volex pvc conduit fed the downstairs lighting circuits. So I would suggest be very careful, take nothing for granted. Any one remember above product? Is it still about?
 
Marty203 are you sure you are not getting mixed up with maisonettes as I could then understand if their downstairs lighting conduits came from their bedrooms above. Perhaps if you where a young lad at the time you may of only worked on those parts of a large job and not remembered or recalled the conduit arrangements for the bedroom lighting which should of been cast into the slab?

Im not that old that I cant remember, lol, the projects were high rise council flats, Hounslow and Feltham and a few in the north around Islington and The Barbicon in the east
 
Im QS for nic firm and we have annual visit
and have to jump through hoops
im sure that for small firms, this is the case. Im sure that may outfits choose the jobs that they show their assessors.
I work for a very large M&E firm, with over 800 tradesmen on the books. I work out of a satellite office, where im one of 8 sparks. As you can tell, im not a fan of the current system of QS. Its not effective in a large firm, where nobody ever see's my work.
 
im sure that for small firms, this is the case. Im sure that may outfits choose the jobs that they show their assessors.
I work for a very large M&E firm, with over 800 tradesmen on the books. I work out of a satellite office, where im one of 8 sparks. As you can tell, im not a fan of the current system of QS. Its not effective in a large firm, where nobody ever see's my work.

i thought we were a large firm with 140 employees m and e. a/c and security devisions ect but would agree that you tend to pick and choose work from the "better" guys to show them
 
Question guys: this is a maisonette with 2 floors undergoing a rewire. How to wire the lights on the lower floor? Options are 1) battening and 2) chase screed above and drop through floor. Everyone seems to prefer option 1 but me! Why is it so hard, especially as we'll be chasing the screed to lay pipework for central heating?
Are there any regulations against running lighting cables in the screed above?
 
Question guys: this is a maisonette with 2 floors undergoing a rewire. How to wire the lights on the lower floor? Options are 1) battening and 2) chase screed above and drop through floor. Everyone seems to prefer option 1 but me! Why is it so hard, especially as we'll be chasing the screed to lay pipework for central heating?
Are there any regulations against running lighting cables in the screed above?


Seeing as you'd be running a cable installation from one installations equipotential zone into another installations equipotential zone, what do you think??
 
Last edited by a moderator:
If this is a maisonette with 2 floors and he's wiring the lower floor lights from the upper floor how would he be running a cable installation from one installations equipotential zone into another installations equipotential zone, or am I missing something?
Seeing as you'd be running a cable installation from one installations equipotential zone into another installations equipotential zone, what do you think??
 
it's a 2 story, ex council, 1960s built flat. with brick walls, concrete floors, and MICC cabling (to be ripped out for the rewire).

see pics.

FloorPlan.jpgzIMG_0422.jpgscreed.jpg

structural report

Visual Observations

• At first floor level, adjacent to the stair well is a small airing cupboard with a water tank. The floor in this area was lifted to reveal a soft grey material, which on first impression was thought to be a floor screed.

• With the aid of a chisel, the soft grey material was easily broken away to reveal a water pipe buried within it.

• The depth to the bottom of the copper pipe was approximately 30mm.

• Below was a further pipe.

• It is believed that the two pipes are the flow and return to the water tank located within the airing cupboard.

• The depth of the screed is therefore most likely approximately 50mm in depth.

• The ceiling of the ground floor reception room was also exposed in one location to reveal a smooth concrete surface, of different colouration and texture to the soft grey material observed within the airing cupboard.

Figure 1 – Exposed Screeded Slab Surface – Airing Cupboard

Conclusions/Recommendations

Based on our visual observations, it appears that the floor structure is of reinforced concrete construction. It was not possible to conclusively determine if the floor slab was of precast or in-situ construction. Based on the surface finish to the soffit area exposed, it would suggest that the floor slab is most likely of pre-cast concrete construction.

To the top surface of the concrete floor slab is quite clearly a screed of approximately 50mm in depth, which has services within it as was seen in the airing cupboard.

We understand that you wish to run further new services within the screed layer. We can confirm that this will not affect the structural performance of the concrete floor slab. However, it should be ensured that the screed is broken out carefully (not with an angle girder or similar) to ensure that the concrete surface of the floor slab is not damaged or cut into.
 
If this is a maisonette with 2 floors and he's wiring the lower floor lights from the upper floor how would he be running a cable installation from one installations equipotential zone into another installations equipotential zone, or am I missing something?


Yep, your right, and that's fine if it's a two storey maisonette and he's using the screed on the upper floor to run his cables in, for the lower floor. Not too sure what he's going to do for the upper floor lighting though?? ..lol!!

My only worry would be, that the surveyor mentions that the floor slabs are of the precast type. Making penetrations in precast concrete slabs, need to be undertaken with caution, especially if they are of the pre tensioned variety!!
 
Not too sure what he's going to do for the upper floor lighting though?? ..lol!!

it's the top floor maisonette, upper floor lighting run above plasterboard ceilings (no concrete)

My only worry would be, that the surveyor mentions that the floor slabs are of the precast type. Making penetrations in precast concrete slabs, need to be undertaken with caution, especially if they are of the pre tensioned variety!!

he said he was unable to determine, and IMO he was not the sharpest tool in the shed. are these photos any help in determining the construction?

IMG_4561.jpgIMG_4565.jpgIMG_4566.jpgIMG_4568.jpgIMG_4569.jpg

those are the pipes that punch through the floor to go to the gravity water tank. notice there is a brick laid in the middle of the concrete! WTF?

that looks poured-in to me, not precast. any opinions?
 

Reply to chasing into concrete screed floors - a risk to the neighbour's lights? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top