Discuss Choosing the correct ballast? in the Commercial Electrical Advice area at ElectriciansForums.net

Well I did look into this and the 4ft lamps are around 1215mm in length, wouldn't this be to big for the 1200mm x 600mm module? Well the guy has changed the lamps he said and the starters and still doesn't work. Can only assume it's will be the ballast, there are 2 ballasts as you said 2 lamps per one, if they are 3ft 30watts each what wattage ballast would i need and same with the 4ft 36watts? (But surely the lamps would be to long for the fittings itself?
If you search for 1200 x 600 modular T8 fluorescent then you will find most are 36W tubes. There is normally hardly enough room to get the tube in place.
Magnetic chokes are becoming harder to get now but you would want a 36/40W choke like this.
For a twin system with HF electronic ballast you would be looking for a 2x36W electronic ballast like this, however they come in different sizes from different manufacturers and you would need to ensure you have space.
I do not know where you would get 2x30W ballasts but you can google it.
Check what you need first.
 
I've changed far too many fluors and you will find sometimes in 4' tubes there is one ballast. If one tube is not in correctly the rest wont work. Getting the bi pins to the precise position (quarter turn) is an art especially on older fittings. Also quite often it is easy to put in the wrong starter. And getting a quality starter is another little trick. It may be the tubes were not put in correctly or the starters are crap such as FSU universal starters which seem to work with nothing. There are different types of starters for single and double ballast tubes. I find Crompton s10 and s16 fairly reliable and seem to work ok. Denmans starters are a waste of time. So having checked that, personally I don't replace ballasts by the time I have fecked about taking out and getting the right ballast and putting it in to find it all still does not work as the end caps are damaged and the time to do it etc. it is cheaper to replace the whole fitting. In my case we have a store and plenty of fittings, high freq. to replace the older starter types. We are not allowed to put in old starter types due to someone suing for epileptic fits caused by a flashing/failing tube as H.F. fittings don't do that. Right that's enough now.
 
Last edited by a moderator:

Reply to Choosing the correct ballast? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi: I am the custodian at Peru Public Library, Peru IL. About 20 years ago, I installed about 150 new General Electric brand electronic ballasts...
Replies
1
Views
1K
Hello gents I'm just after some clarification, I have a kitchen light fitting that uses a 2D 28W compact fluoresent lamp that I'd like to...
Replies
3
Views
1K
I want to operate 3 lighting set up using metal halide lamps for studio works or cinematic projects in the future. as of now i have got two...
Replies
0
Views
1K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
I have looked a small office refurb where currently installed are recessed 2x 26w PL CFL's (about 50 in total). Client doesn't want to replace...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top