Hello everybody! I just wanted to ask, what would be the best practise to run circuits for white goods?
In my plan what i see is:
1. Fridge & Freezer 20 amp RCBO radial wired with 2.5mm
2.Washing machine 20 amp MCB Radial 2.5mm
3. dish washer 20 amp mcb radial with 2.5mm
4. Washing machine and dish washer 32 amp mcb wired 2.5mm ring final.

Please advice what is the best practise to do it? would it be too much having dish washer and washing machine on separate circuits or just wire them both on ring final?

Also advice me please with mcb sizes if i am correct about radials. As far as i rememmber from regs maximum mcb rating for radial is 16amp.

Thank you
 
If this is a domestic set up, a single 2.5mm2 radial fed by a 20A RCBO is adequate for all three, if the water heating elements in the dishwasher and washing machine are 2kW.
If either are 3kW, then a 4mm2 radial fed by a 32A RCBO will do, but the washmac. and dishwasher shouldn't both be plugged into the same double 13A s/socket.
 
Also advice me please with mcb sizes if i am correct about radials. As far as i rememmber from regs maximum mcb rating for radial is 16amp.
The only maximum rating for a MCB is either the:
  • cable overload limit
  • fault clearing Zs value, or
  • whatever a specific load requires.
There is no "radial" limit as such. With 13A sockets you already have a load-limiting fuse in the plug so it comes down to adequate cable protection.

Personally I would just put the lot on a 32A RCBO for a ring final circut as at least if it trips you have more feedback it has gone, rather than waiting until some time later to find the fridge has been off for ages and nothing else is showing a fault. Or get a fridge alarm!

But as mentioned above make sure all of the feed points have accessible means of isolation. So ideally double-pole switches feeding an un-switched socket if it has to be behind the appliance. You don't need DP for powering it down safely, but you do if you want to prevent a N-E fault causing RCD troubles.
 
Last edited:
Thank you for your replies guys, my last question would be how does kitchen grid nswitches are wired? does they have to be on the ring? and linked between each other? or i can wire them on radial? dedicated load to each switch?for example dedicated load from CU to fridge freezer switch,then dedicated load to washing machine switch, and etc?
 
Grid switches are just modules that clip in to a support template, and then fit behind the faceplate. They are not wired internally, you have to do that.

Advantage is the look neat and you can mix and match them.

Disadvantages are they are tight in there (you need a deep back-box and care to wire up) and some folk have had issues of them burning out more than the full-size 20A switches do.

Typically they will take a single 4mm cable, or 2*2.5mm, but that is about it. So on a typical RFC you can link the supplies to each switch in the loop. But again needs a bit of care.
 
If you were doing a grid-switch for the lot you might as well run it as a 4mm radial on 32A and then put some 5-way wago joints in the back of the box to fan it out on 2.5 to each switch.

It might be the switchs take 2*4mm but I would try it out before committing.
 
Just corrected an earlier post to say I would use an un-switched socket with a separate switch. No real need for two switches and it is just another thing to forget to put "on" before pushing a washing machine back, etc.
 
You can use them as any normal switch, so if you want each on a radial feel free to do so.
Thank you! So if i run 2.5mm radial from rcbo 20A to one switch,labeled as washing machine then run another 2.5mm radial from another RCBO 20a to another switch labelled dish washer. WIll that be good practice?
 
Thank you! So if i run 2.5mm radial from rcbo 20A to one switch,labeled as washing machine then run another 2.5mm radial from another RCBO 20a to another switch labelled dish washer. WIll that be good practice?
Yes, that is perfectly good practice.

The RFC versus a few radials argument with run and run, but what matter is each circuit is safe & adequate for the load(s) and correctly labelled.
 
I seems a lot of circuits for a kitchen. What about general sockets for kettle, toaster, etc?
In general, diversity has a big say in final loading, taking into consideration what's going to be used regularly at the same time.
Unless it's an outsize kitchen, one RFC and, maybe the odd radial, would be my option.
How big is the house and how big a CU do you want?
 
I tried the grid switch route with neons to indicate they were on, the switch's where engraved with the function of each circuit, but in the end it became too busy inside the 35mm back box and I resorted to radial circuits for each appliance, this was in France where radials are the norm, in the UK I run all of the white goods off an RFC, sockets in the back of a tray space so no need for switches above the worktop.

But if you must:
 

Reply to Circuits for white goods in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
872
I've purchased a horizontal unvented cylinder that has come with 2 immersion heaters. I was hoping to use the same circuit the my existing tank...
Replies
16
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
787
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top