Discuss Class 2 insulation tests in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

We are having very similar problems testing our Class 2 items, can anbody tell me the difference between a standard class 2 test that covers insulation, leakage and load and a touch leakage test that only covers insulation and touch leakage.
 
Class 2 equipment has double or reinforced insulation around the live parts. exposed metalwork should never be able to become live unless there was a major fault that would be visually obvious. That is what i was taught anyway. Dont know where they are coming from with that utube clip.

Yes; but insulation can deteriorate with age and use or could be damaged (hairline crack and moist environment) leading to a leakage path to exposed metalwork? Building sites are notorious ...
 
Thanks. I did have this book when I did the 2377 course. But l can't find it atm. All I'm really trying to find out is how to carry out insulation test on class 2 items both with exposed metal parts eg. Drills, hairdryers etc without exposed metal parts eg. Phone chargers, class 2 detachable leads, radios etc.

The book you need is the Code of Practice for In-service Inspection and Testing of Electrical Equipment, 3rd Edition.

For Class 2 insulation test, connect live and neutral together so you can then test the insulation resistance between live conductors and any exposed metalwork or suspect point on the insulation (there can be a conducting material deposited on the surface of the insulation). Probe between the live conductor common point and any exposed metalwork or suspect joints on the outside of the equipment under test.
 
Hi - just seen this post. Testing Class 2 appliances does cause a lot of confusion, and there has been a lot of debate on other forums about this issue.

When the insulation test is carried out on an appliance, we're checking for a breakdown of insulation between live/neutral and the metalwork on the appliance. So, for example, on a drill we'd be checking to see if the chuck/drill bit would be live when we operate it.

The important point here is that live and neutral are joined together inside the tester (so that there's no potential difference between them) and we measure any breakdown of resistance by putting the probe (clip) onto a metal part of the appliance. This is different from installation testing on a building (PIR) where an insulation is carried out BETWEEN live and neutral.

If you think about it, this is why electricians have to go around unplugging all the appliances and removing all the light bulbs before an insulation test between live and neutral, and why a drill doesn't start up when we insulation test it during a PAT Test.

The clip HAS to be attached to a metal part in order for the test to have any value. If there is a breakdown of insulation, current will flow back down the test lead and so the PAT machine will indicate a fault.

On the same token, if we don't connect the clip to anything at all, no current will flow down the test lead, and a PASS will be indicated, even though we're not testing anything! I have witnessed some so called 'professional' PAT Testers testing things like wall wart power supplies by plugging them in, pressing the insulation test button, and then 'passing' them when the insulation test comes back as a pass!

If there is no metalwork on the appliance (such as a plastic hairdryer or a laptop power supply) then there is no need to do an insulation test. And, because it's Class 2, you don't need to do an earth test either, which is why we say that an inspection is ALL that is required on a Class 2, plastic appliance.

If you have a Class 2 appliance with some metal parts the you will need to carry out a full inspection, followed by an insulation test.

It is normal practice to refer to Class 2 appliances with metal parts as 'DOUBLE INSULATED' and those with all plastic parts as 'ALL INSULATED'

Hope this helps!
 
Yes; but insulation can deteriorate with age and use or could be damaged (hairline crack and moist environment) leading to a leakage path to exposed metalwork? Building sites are notorious ...

This is a good point, but a 500V insulation test won't normally detect this sort of fault. In the early days of PAT Testing we used to carry out FLASH TESTS to detect this sort of fault, but this isn't recommended now unless a repair has been carried out. I have seen people wrapping appliances in tin foil and then doing the insulation test - again completely pointless.

Modern manufacturing standards take account of things like hairline cracks - so that if there was a tiny crack which wasn't visible then it wouldn't be dangerous. Any more obvious physical damage or moisture in the appliance would be picked up by the Visual Inspection - providing of course this is done properly by the tester and he/she doesn't dive straight in and test it without looking VERY carefully at the appliance first!
 
Hello,
So if I have a household appliance which has a plastic enclosure and there are only 4 metal screws fixed in this enclosure (metal screws don't touch any live or neutral conductors) I have to check the insulation resistance by touching all of these 4 screws one by one? Am I right? Or this insulation test is not needed then?

Thanks in advance for answer.
 
You need to use the probe to test the insulation where users are likely to touch the appliance. So you put 500v down the line and neutral and see how much comes back through the insulation. Screws are conductive so it is worth running the probe across the screws.
The insulation on a class 2 appliance is a method of fault protection as well as basic protection, so this should be tested.
 
Delongie have a convector heater that has a metal cover but 2 plastic side panels with a class II badge on it so I put the probe on the metal frame to confirm there is no leakage but even then I flicked the tester to class I to make sure there was no continuity but in the case of a plastic hoover then there is no point doing a insulation test yet speak to PAT tester and its yep plug it in and push the button now that worries me because they dont understand without the earth lead there can be no return path. The only other problem as i have is because the industry is full of Urban Myths so you now get a caretaker saying either well the last guy tested it or I have been told you dont have to test class II equipment mind I was lucky as an older Delongie class I heater was sitting beside ther class II model so I could explain to the customer
 
Hi, Class II (and Class I) insulation test is carried out with Live and Neutral shorted together. With Class I the return path is the Earth connection - IF THERE IS A FAULT. With Class II the return path is any user touchable metal part. When testing a phone charger, the test lead crocodile clip needs to be clipped to the metal jack. Otherwise if there was a fault, this could be missed.
 
Last edited by a moderator:
Hi, Class II (and Class I) insulation test is carried out with Live and Neutral shorted together. With Class I the return path is the Earth connection - IF THERE IS A FAULT. With Class II the return path is any user touchable metal part. When testing a phone charger, the test lead crocodile clip needs to be clipped to the metal jack. Otherwise if there was a fault, this could be missed.

Welcome to the Forum Mistertee... when wanting to reply to a thread just check the dates of the previous postings, this is a 3yr old thread so unlikely any responses to your post from the OP.

Closing thread on that note :), feel free to open a new thread if your are interested in discussing this subject :smiley2:
 
Last edited:

Reply to Class 2 insulation tests in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
493
I am a new PAT tester for a school, and I am stuck testing a plasma globe. It has a two core wire going to it, but no class 2 mark on the...
Replies
18
Views
2K
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
747
Hi all! I am looking to sell some used electrical items (eBay), and am considering (unlike the vast majority of eBay business sellers) testing...
Replies
16
Views
2K
Sorry if this thread is in the wrong section, I was always led to believe that a TV was class 1 for PAT testing, however the TV has a metal earth...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock