Discuss Class 2 metal fitting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
8
Bought 2 metal wall lights arrived today and just opened them.

They are completely metal in construction states on the fitting they are class 2 and have no earth connection.

The cables leaving the chocbox inside to the lampholder are single cores.

How can this be class 2?
 
The top hole leads to the lamp the bottom to one of those twisty spiral bedside lamps you get in hotel rooms.

Yeah it is sheathed at the top but not the bottom and neither are the brown and blue you can see.
 
I've seen fittings like this before. The wedge shaped spotlights for under kitchen units. Marked as Class II, but wholly metallic. One loose cable and you've got a live metal block, easily touchable.
Cannot be classII unless the connection is made within a plastic box, within the metal fitting.
 
looking at the photo, is it a "grey" import?
 
It is odd one pair is sleeved but the other is not but it may not be relevant if the conductors have reinforced insulation. Needless to say the claim for double insulation is somewhat tenuous.
 
Sometimes the individual brown and blue have a clear (not always obvious) sheath making them double insulated and therefore Class 2 (As long as the connector is within its own insulated enclosure).
 

Reply to Class 2 metal fitting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
For the bathroom, want them matching and one needs to go over the shower. Also need to be ok with insulation over the top. Ideally fit in the...
Replies
2
Views
265
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
20
Views
2K
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
976
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
660

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock