Morning fellas. I know from regular visits to this website that we have some rather intuitive Sparkie’s on here so I thought I’d join in the fun.
I’ve got a rather basic question to start with but also where some of you can hopefully show your tips and tricks.

Im currently working on a project, making pre fab elec cupboards. These cupboards only have 1 circuit on the fuse board, until this is added to on site. The circuit consists of 17 points, only 3 of which are sockets, the rest being switched fused spurs and only 7 of these have loads installed in the factory. I do all the dead tests at source but unfortunately I don’t do all the installation as there are 5 other “Sparkie’s” (use the term loosely) on site. It’s becoming rather a pain removing all the spur fronts to do my ring final test, fully and properly. Now I’m more than willing to accept that I am being dumb, which I’m sure a few of you will be more than willing to point out, but do you guys have any ideas as to short cuts I could use to make the whole process a lot quicker?

Any ideas, opinions, legal short cuts welcome.

Thanks fellas.

This is my first post as well so hopefully it’s not too brutal an introduction. cheers boys!
 
Not the only odd feature of this particular install I might add! Designed by, lets call them, non Sparkie’s.

It will literally just be R1 + R2 and polarity. No live testing. This will be carried out on site once unit is powered up. My tests are literally to confirm cable wiring and insulation are correct before the units leave the factory. I’ve been told to just test the sockets but I’m not prepared to do this as it does not confirm polarity is correct at any of the remaining 14 spurs.
 
Welcome to posting on the forum.
Initially I am think electric screwdriver for speed, but you probably already do that.
If you can get to the cupboard earlier in the assembly so that the spurs are wired but not fixed back yet and do, perhaps, just the ring continuities this may work.
If you have loads attached then on some loads it is easier to get to the connections at the load end and you can then take account of the resistance of the supply cable (which should be minimal in your case).
If the spurs are all the same and you know where the terminals are and this is a repetitive task then you could make up a custom test probe bracket that can automatically access the terminals when the spur is just pulled a short way from the wall, but you may find getting the probes in the right place slower than taking it off entirely.
probe bracket.jpg
 
just awaiting Megger's invention of a wireless probe system. just put a fob in close proximity of the spur and the new MFT will give a wi-fi read out of all you need. then the fob on your ipad can read off the MFT and enter the readings on the EIC. happy days.
 
Not the only odd feature of this particular install I might add! Designed by, lets call them, non Sparkie’s.

It will literally just be R1 + R2 and polarity. No live testing. This will be carried out on site once unit is powered up. My tests are literally to confirm cable wiring and insulation are correct before the units leave the factory. I’ve been told to just test the sockets but I’m not prepared to do this as it does not confirm polarity is correct at any of the remaining 14 spurs.
If you have been told to only test the sockets then I am baffled why you are not happy to do this? Just make a note on the certificate that you have only tested the sockets ,or have I misunderstood?
 
Can you get to the live terminal by popping the fuse out and sticking a prove in to the fuse holder? And the earth via a faceplate screw? That would give you R1 R2. The resistance might be slightly higher through the screw though so you would have to compare.

EDIT: Actually, thinking about it, im not sure if the fuse holder stops you accessing the actual live part behind
 
Thanks for the responses. Keep them coming. I like your way of thinking.
Unfortunately the people telling me to just test the sockets have absolutely no idea of the reason behind testing and the implications of getting it wrong or not doing a thorough job. They are plumbers, need I say anymore. They’ve got the contract for these utility pods because they also contain a boiler. As I said in previous message, just testing the sockets isn’t going to give me any indication as to the correct polarity of the spurs. I currently whip them off with a battery screwdriver and to be honest it doesn’t take me too long it’s just an inconvenience rather than a flat out problem. Testing via the fuse carrier and screw isn’t an option as it’s a plastic dado trunking system so there are no earthed metal back boxes to get a reading off. Testing the load side is an option but like I say this is only 50% of the spurs that have a load fitted, the other 50% being installed when they go out to site. I guess I’m just being lazy and will need to continue with the old fashioned way. I’m always looking for more productive ways of doing things but I guess sometimes there just isn’t one.
 
Actually now I think about it the screw will have a connection to Earth regardless of the metal back box, so your way may be plausible, providing there is a good connection to the line conductor via the fuse carrier. I’ll give it a go tomorrow and see what it comes back with. It may be a slightly higher r1+r2 reading but one thing it will confirm is correct polarity. Top marks for that man!
 
No they are currently just flex’s coming out to final position which I’m aware I can just test the ends of and deduct the overall resistance of the flex from final r1 + r2. It’s more the spurs that have no loads/flex’s connected that I’m concerned with
 
Can you tell production not to screw the face plates into position just leave the screws attached to the face plates; Once testing is completed you can then put them on only rather than both on and off and would speed up production further back in the line as well.
 
No they are currently just flex’s coming out to final position which I’m aware I can just test the ends of and deduct the overall resistance of the flex from final r1 + r2. It’s more the spurs that have no loads/flex’s connected that I’m concerned with

How long are the flexes?
 
I could do mate yeah, it’s just some of the people we are working with really couldn’t even be called Sparkie’s and that’s without even mentioning the plumbers! There’s a couple of flexes that would have negligible impedance so could be disregarded entirely to be fair but there’s also a couple of 4/5 metre ones that would just need deducting from reading
 
To be honest it’s not a great hardship to continue what I’m doing but like I say I’m always looking for ways to be more productive so I thought someone may have thought of an intuitive way to overcome it
 
Actually now I think about it the screw will have a connection to Earth regardless of the metal back box, so your way may be plausible, providing there is a good connection to the line conductor via the fuse carrier. I’ll give it a go tomorrow and see what it comes back with. It may be a slightly higher r1+r2 reading but one thing it will confirm is correct polarity. Top marks for that man!

I always use an exposed conductive part to gain a Zs reading. It proves the exposed metal work is earthed and also provided the highest value Zs likely to be present on the circuit.
 
If you have been told to only test the sockets then I am baffled why you are not happy to do this? Just make a note on the certificate that you have only tested the sockets ,or have I misunderstood?
Electrician is a professional job so you have to take responsibility for doing things right sometimes. You answer to professional responsibility as well as the customer
 
Electrician is a professional job so you have to take responsibility for doing things right sometimes. You answer to professional responsibility as well as the customer
You have to do things right at all times not just sometimes. You are only responsible for what you have agreed with the client and you just need to record this on the certification that you give to the client. If you want to perform tests that you haven't been asked to do then you are free to do so but you won't get paid for it.
 
You have to do things right at all times not just sometimes. You are only responsible for what you have agreed with the client and you just need to record this on the certification that you give to the client. If you want to perform tests that you haven't been asked to do then you are free to do so but you won't get paid for it.

For a periodic I totally agree but not for an initial verification. If you explain to the customer why they need it then youll get paid. Plus sometimes you have to do things you won’t get paid for, for your own piece of mind.
 
An initial verification has to be carried out in full, in the correct order at all times in my opinion. A periodic you have a lot more flexibility due to the fact that 9 times out of 10 you’ll have various circuits that can’t be turned off and therefore certain tests your unable to carry out. But like I say, with an initial I always try to carry out a complete test in the order stated.
 
My point of view exactly John. If we don’t do things responsibly and properly, people die.
If there was a fault on a different part of the installation the blame would be on the client who
You have to do things right at all times not just sometimes. You are only responsible for what you have agreed with the client and you just need to record this on the certification that you give to the client. If you want to perform tests that you haven't been asked to do then you are free to do so but you won't get paid for it.
An initial verification has to be carried out in full, in the correct order at all times in my opinion. A periodic you have a lot more flexibility due to the fact that 9 times out of 10 you’ll have various circuits that can’t be turned off and therefore certain tests your unable to carry out. But like I say, with an initial I always try to carry out a complete test in the order stated.
i agree with you and if you have installed the wiring and you are doing the testing you have no flexibility regarding the tests and should do them in the prescribed order. I was under the impression that the issue was just the testing of the units when someone else had done the wiring,in which case I would just test the sockets and note this on the certificate
 
To be honest I would do a full test under both circumstances. But IF I was to choose one then I would be more inclined to not test my own work as I know I’ve done it correctly. That being said I would still test it in full because no one is infallible
 
You have to do things right at all times not just sometimes
Agree, perhaps i should have said sometimes there's a difference between the two!
You are only responsible for what you have agreed with the client and you just need to record this on the certification that you give to the client.
True but the client or your plumbers are not qualified electricians so whatever they say doesn't override the correct way of doing it. That's the difference between a professional and a labourer.

The labourer just does what they're told and the bar for negligence is quite high. But for a professional you have a duty of care and when someone is killed or injured saying you wrote it on the form probably wouldn't go down too well.


Whenever any major incident happens, there is always a long chain of small passing of responsibility, and someone has to stand up for the right way. If it isn't of consequence, then it'll be ok, but knowing the purpose of testing and still noting limitations knowing that dangerous electrical installations could be put into use surely isn't professional behaviour?

Ok if after arguing the point with the bosses they are adamant then maybe, but it shouldnt be just go home thinking a good days work completed.

Edit sorry for the long post!:rolleyes:
 
You might be able to solder a fine flexible insulated wire ( say a few cm chopped from a headphone cable) onto the end of a fuse, and use that as a probe to make an adequate contact with the fuse holder which might now be able to almost close. ( The wire will jamb). It will depend on the particular brand/ design. Not something I've ever tried mind you.
( For dead test only I would add!)
 
One of the reasons for the R1+R2 test is to check it is a ring, can you not physically see the ring? You could always test at the flex pulling the fuse will prove fuse in the live. The other fused spurs the only way to take off spur.
 
Can you get to the live terminal by popping the fuse out and sticking a prove in to the fuse holder? And the earth via a faceplate screw? That would give you R1 R2. The resistance might be slightly higher through the screw though so you would have to compare.

EDIT: Actually, thinking about it, im not sure if the fuse holder stops you accessing the actual live part behind

I heard a tip before that you can jam a small screwdriver (2.5mm slotted) into the fuse carrier and get a reading off of the shaft. Never tried it however. I suppose its success largely depends on the design of the FCU.
 
Last edited:

Reply to clever ways of ring final test without removing spur fronts?? in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
Hi all, I had a fault on site today I've not encountered before. if anyone could shed some light on a similar fault they may have encountered...
Replies
9
Views
2K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock