Discuss Coding advice on EICR please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Looking for some advice as im fairly new to EICR reporting, although have passed 2394/95 and have carried out a couple of straight forward reports.

Firstly, on a EICR I have carried out for a family member I have found an old MEM memera 2000 metal clad consumer unit, over 8 years old. I was wondering if this is acceptable as fulilling fire rated properties of consumer units to 17th edition (I have a feeling it might not be?), or would be classed as C3 as not complying with current regs even though it is metal clad? I would imagine it has not been tested to same standards as current metal clad boards?

Secondly whilst carrying out testing on the ring main of the above board, the RCBO test button would not operate properly (once in about 5 attempts) so clearly an issue. My feeling is that it is probably a C2 and would deem the EICR as unsatisfactory, but wondered whether there was an argument for coding it C3 as lack of an RCD in this scenario would only merit a C3 anyway? The RCBO in question passed all other tests.

Finally, in regards to fixing any issues (if RCBO test button issue is C2), can I speak to the client, replace the RCBO and issue the satisfactory EICR, or would I have to go through the process of failing the EICR, replacing the RCBO and reissuing another EICR, or even just a minor works?

Apologies for such a long question. Any help would be greatly appreciated.
 
When doing an EICR, you have to bear in mind the age of the property. If what's there now complied with the regs at the time, then I would not code it, provided the DB is in good condition ie no unblanked holes etc.
If there rcbo is present and has failed...C2
If your doing the work for family, then I would replace the faulty rcbo and test its operation, as opposed to failing it first on the report, no different to having an mot on you car, noticing a brake light is off before you take it, replace bulb why let it fail first?
 
You mention "old" MEM Memera 2000, at 8 years it's a baby compared to what ive come across still in
use...
..IMG_0004.JPG
Not the actual board but I've had to do EICRs on similar!
 
EICRs do not fail they are either satisfactory or unsatisfactory. If you have a Memera 2000 rcbo then by all means replace it if the client is happy with this.
 
When doing an EICR, you have to bear in mind the age of the property. If what's there now complied with the regs at the time, then I would not code it, provided the DB is in good condition ie no unblanked holes etc.
If there rcbo is present and has failed...C2
If your doing the work for family, then I would replace the faulty rcbo and test its operation, as opposed to failing it first on the report, no different to having an mot on you car, noticing a brake light is off before you take it, replace bulb why let it fail first?

Yes it is in good condition, I just wondered whether it would been tested to the same fire rating standards as a newer metal clad board, and that by indicating C3 it would be evident that it is an older board and would not be something we would install now. I will most likely not code it unless I see any relevant info stating otherwise.
 
bottom line here is:
1. is it safe for continued use. no code
2. is there a n imminent danger. code 1
3. is there a potential danger, code 2.
4.could an improvement increase safety.code 3.
 
When doing an EICR, you have to bear in mind the age of the property. If what's there now complied with the regs at the time, then I would not code it

I can't agree with that at all for several reasons.

Periodic inspection is to be carried out using the current version of the regs as the standard of safety.
How is one to reliably establish exactly when something was installed and therefore whether or not it complied ?
How is an inspector expected to have a detailed knowledge of all previous editions of the regulations with which to assess previous installations to ?

An example of the above points.
Today I removed a fuse board from the 1940s/50s that was supplying the lighting circuits in an old house. None of the circuits had cpcs, the neutrals were fused, the wooden door could be opened without a tool or key and the fuses could similarly be removed. With fuses removed live parts were accessible that were easily touched.

It could well be that all that complied when installed, but had I successfully established this by accurately determining the install date and checking the relevant regs, would I be right in saying no codes were appropriate ?
 
I can't agree with that at all for several reasons.

Periodic inspection is to be carried out using the current version of the regs as the standard of safety.
How is one to reliably establish exactly when something was installed and therefore whether or not it complied ?
How is an inspector expected to have a detailed knowledge of all previous editions of the regulations with which to assess previous installations to ?

An example of the above points.
Today I removed a fuse board from the 1940s/50s that was supplying the lighting circuits in an old house. None of the circuits had cpcs, the neutrals were fused, the wooden door could be opened without a tool or key and the fuses could similarly be removed. With fuses removed live parts were accessible that were easily touched.

It could well be that all that complied when installed, but had I successfully established this by accurately determining the install date and checking the relevant regs, would I be right in saying no codes were appropriate ?
Any photos of the board?
Never seen one with a wooden door.
 
I can't agree with that at all for several reasons.

Periodic inspection is to be carried out using the current version of the regs as the standard of safety.
How is one to reliably establish exactly when something was installed and therefore whether or not it complied ?
How is an inspector expected to have a detailed knowledge of all previous editions of the regulations with which to assess previous installations to ?

An example of the above points.
Today I removed a fuse board from the 1940s/50s that was supplying the lighting circuits in an old house. None of the circuits had cpcs, the neutrals were fused, the wooden door could be opened without a tool or key and the fuses could similarly be removed. With fuses removed live parts were accessible that were easily touched.

It could well be that all that complied when installed, but had I successfully established this by accurately determining the install date and checking the relevant regs, would I be right in saying no codes were appropriate ?
I was referring to the item the OP mentioned about the DB being suitable for fire rating.
Obviously a degree of common sense has to be applied during EICRs, and if I came across anything as shown in the pictures....then it would be deemed unsatisfactory for several reasons.
This is where judgement has to be applied....
 

Reply to Coding advice on EICR please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
407
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
1K
Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
890

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock