My customer is having his supply upgraded from 3ph 80a per phase to 160a per phase. This will obviously require 50mm metre tails. I will also upgrade the bonding etc. The building currently has 2 DB's with 100a 3 pole main switches in the utility cupboard.
Should I install two MEM 200a 3ph isolator switches (change fuses to 100a). Bring in the 50mm tails then send 25mm tails from the isolator to the DB. Or is there any other way around this.