Hi I am a domestic installer mostly install bathroom circuits showers and such but I have been asked to rewire Commercial storage unit there is a 3 phase consumer unit already in place with no m.c.b’s in it but my question is will I need to remove the main isolator and replace it with a R.C.D similar to a residential property or put RCBO’s instead of MCB’s as I am a bit rusty on the regs for commercial properties Thanks for any help
 
Unless you have a split load RCD board, you only option is for the installation of RCBOs on circuits that require them.

The regs are the same regardless of the installation they are being used for.
 
definitely NO to replacing the incomer with RCD. as dilb says, decide which circuits require RCD protection and use RCBOs for these. bear in mind the phrase " skilled or instructed persons".
 
Unless you have a split load RCD board, you only option is for the installation of RCBOs on circuits that require them.

The regs are the same regardless of the installation they are being used for.


Never seen a split load 3 phase db.

Come to think of it, never seen a 3 phase consumer unit :confused:
 
Hi I am a domestic installer mostly install bathroom circuits showers and such but I have been asked to rewire Commercial storage unit there is a 3 phase consumer unit already in place with no m.c.b’s in it but my question is will I need to remove the main isolator and replace it with a R.C.D similar to a residential property or put RCBO’s instead of MCB’s as I am a bit rusty on the regs for commercial properties Thanks for any help
There is more chance of winning the lottery every day for the rest of our lives than answering that, what earthing arrangements? what connected loads? answer that then we can help
 
Never seen a split load 3 phase db.

Come to think of it, never seen a 3 phase consumer unit :confused:


My house in Cyprus has two of them!! They are as common in domestic installations as single phase consumer units in Cyprus as well as in many other countries too....

But like yourself, never seen a split load 3 phase CU/DB. They would all incorporate RCBO's where RCD protection is required. Which to my mind, is a far better practice anyway, than single RCD's looking after several circuits....
 
Some DIs can't get cover for three phase work
I am a full scope member with napit time served electrician with 2391 and 17th edition 12 years experience but I only seem to do domestic properties but want to move to commercial properties too but not done to many of them in the last 12 years.
 
I am a full scope member with napit time served electrician with 2391 and 17th edition 12 years experience but I only seem to do domestic properties but want to move to commercial properties too but not done to many of them in the last 12 years.
I stand corrected along with everyone else. Sorry mate.
 
I am a full scope member with napit time served electrician with 2391 and 17th edition 12 years experience but I only seem to do domestic properties but want to move to commercial properties too but not done to many of them in the last 12 years.

Well you're not a domestic installer then surely
 
I am a full scope member with napit time served electrician with 2391 and 17th edition 12 years experience but I only seem to do domestic properties but want to move to commercial properties too but not done to many of them in the last 12 years.
It's a completely different cup of tea, I have seen it all regarding Domestic sparks trying to just do commercial / Industrial work and they always fall short, when you can draw a star delta diagram and connect up a motor which is 3 phase and starter without a drawing you then have a chance, by the way, YEP I CAN DO IT, and I know nothing compaired to some of the sparks here, welcome to the forum lol
 

Reply to Commercial rewire in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
840
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
579
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock