I know every computer/equipment type will have a slighty different earth leakage stated by the manufacturer, however I was wondering what people use as a "rule of thumb" value when designing ring final circuits in offices intended to be used for computers.
I was thinking 1.5mA per computer inc monitor etc?
I always use the high integrity cpc configuration incase it exceed 10mA (543.7.2.201) however 531.3.2 states that it shouldn't really go over 9mA if on a 30mA RCD. Oh well what's 1 extra mA ?