Hi,

Iam replacing my loft insulation to a thickness of 270mm, putting 100mm between the joists and then 270 over the top, then flooring it. I’m Putting 175mm loft legs on top of the joists which are 130mm which should give a slight air gap. My question is there is 20mm metal conduit running single cables to the lights and switches which is sitting on top of the joists, is the conduit permitted to be within the layers of insulation?

Thanks
 
should be OK with lighting as long as the lights are low wattage e.g. LED. however, singles in conduit is ancient. could it be time for a rewire?
 
should be OK with lighting as long as the lights are low wattage e.g. LED. however, singles in conduit is ancient. could it be time for a rewire?
Ought to o be easy to rewire in that conduit. Personally I'd use derating factors for whichever gives worse case (insulation I think) cable rating and adjust accordingly
 
should be OK with lighting as long as the lights are low wattage e.g. LED. however, singles in conduit is ancient. could it be time for a rewire?
Probably will be some sort of led bulbs.. they are the old colours so was thinking about changing them while I was at it, but was just going to keep it singles in conduit?
 

Reply to Conduit and loft insulation? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
185
So I had a ceiling repair done in my bathroom due to water damage. The neighbors toilet above me was leaking for who knows how long. Mold...
Replies
1
Views
714
Hi We recently had an 7kW EV charger installed. Due to the consumer unit being situation within the kitchen of our bungalow, the cable needed to...
Replies
10
Views
4K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock