Discuss Conduit Support in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Looking for some advice if anyone can help.

I've been asked to install sockets in a new build business unit. The company deals with software imaging - lots of computing power but no machinery, tools, etc.

The place is pretty much a standard build with a number of heavyweight vertical RSJ's cross-hatched with U-shaped, mild steel beams onto which a potential plasterboard wall could be fixed. The client is leaving this open, though, so I was hoping to hole-cut through the steel beams and run a 20mm plastic conduit through from one end to the other in an L-shape from the CU on one wall a total length of around 20m.

I'm running a radial circuit for four twin sockets as they are all being placed on this one run. Trouble is, the regs say that rigid plastic conduit has to be supported at 1.5m intervals for a horizontal run, and there's approx. 2m space between these. So, i'm considering fixing a 3x1/2" wooden plate along the length of the wall on top of the steel uprights and then fixing the conduit to that. Steel conduit or tray are options, but I'm trying to keep the price as keen as I can. Can anyone suggest another method?

Thanks

Must be a new regulation that as it is not in mine

Also as you say that this radial is going to be provided for IT equipment do you think that your radial design of 4mm conductors and I assume that is a 4mm CPC and not perhaps even a 2.5mm is perhaps the best
 

Reply to Conduit Support in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Replies
8
Views
720
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
447
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
I've an otherwise small and simple job to do later, out of hours, fit an outdoor IP FSU for a small AC unit fed from an outdoor socket on an RFC...
Replies
12
Views
2K
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock