Discuss Conduits, singles and concrete floors in the Australia area at ElectriciansForums.net

J

JulianC

Evening all.

Next door neighbours' son has just bought a house and I've just been down for a look at the electrics for him. The house is a 1950's terrace with concrete floors both upstairs and down! Chap wanted, amongst other things, a lot of surface mount switches and sockets sinking into the walls. I whipped a light switch box off for a look to find it covering a steel-lined recess in the wall. Upon further investigation it looks like a lot of cables exiting the CU (old steel Wylex type with plug in MCBs) are singles and disappear off into steel conduits running down into the ground floor and up to the upstairs. I therefore suspect the steel lined recess behind the light switch was fixed to the end of a run of conduit.

Has anyone any experience of similar installations? (Concrete floors and singles run in buried conduits). The house only has a single socket ring and I suspect (3 wires in the breaker) that there is a downstairs ring with a spur to upstairs (which only has 2 original sockets by the look of things). I will be suggesting a rewire with 2/3 proper socket rings but am concerned how easy it will be to get T/E to each point. Presumably the conduit runs will be jointed under the floors? What are people's thoughts on using singles in a domestic situation? (It's not something I've come across before)

Thanks and soz for the long post!
 
Dont use the old conduits except prehaps for the switch drop's, run all the cable to the first floor and drop to the ground floor, might sound a lot of work but will be quicker than messing about with the old conduit ( which might even be split conduit which is a nightmare.)
 
out with the chasing tool!!:D hope he hasn't got attached to the floor covering or would sir prefer the mini trunking its all the rage;)
 
once did a pob in the north east, concrete ceiling and floors to all levels. stunk of dogs but made a nice wage off it hourly just there till it was done , food digs and drink all paid for :) strangely enough took a while to complete:)
 
I see;) I have had the lucky pleasure of going through a pipe with a grinder, it was running diagonal across a wall in a room with no rads or water services not fun at all.
 
Last edited by a moderator:
Cheers all. I think in the cold light of morning, it's going to be a lot of chasing - taking advantage of the 150mm zone below the ceiling to get my cables round the ground floor. I'll suggest a nice bit of coving to hide my dodgy replastering.....
 

Reply to Conduits, singles and concrete floors in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
342
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
Hi there - good site. Mrs wants a new socket directly below a light switch on the ground floor (says it will look neater vertically inline)...
Replies
4
Views
1K
I am going to need to install a small amount of galvanised steel conduit, leading down to perhaps 4 sockets and a light switch. This is in a...
Replies
38
Views
4K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock