Hi All,
looking for some assistance on this as finding different information wherever i look.

We have a garage external to the house, which we are turning into a small 1 bedroom flat, due to the layout the shower room will have to be located in the corner where the garage consumer unit is, which is a two way consumer unit, rcd protected with lights and sockets coming off it.

The question is whether I can just build a small cupboard around it with a door, or will i have to partition off the corner so the consumer unit is in a seperate room behind a partitition.

I have found several posts mentioning new builds with consumer units in toilet / shower rooms, but just wonder where exactly i stand with current regulations, I'm in Scotland also.

Look forward to your replies on this.

Thanks
Robert
 
First of all, rooms with just a toilet and basin are not classed as a special location, just “rooms containing a bath or shower”

The regs say everything in this special location has to be rcd protected, so this consumer unit may or may not be.

It’s not so much being able to be touch with wet hands, but how moisture in the air can affect the protective devices through corrosion.
 
Unfortunately it isn't so clear cut.

There are restrictions for rooms containing a bath or shower, in Scotland this includes that switches (such as lights) are prohibited - although pull switches are OK.

However it has been established that anything in a fixed cupboard or enclosure is defined as not within the room. (So booster pumps etc can be underneath the bath tub as long as it's enclosed.) Also non-switching things such as fixed equipment like showers, macerator units etc are OK.

This means that there isn't any rule prohibiting consumer units inside a room containing a bath or shower, as long as its within some enclosure such as a cupboard.

However many people including some electricians just don't like it, and fall back on general "catch all" regulations such as "suitability for the environment " - which may be correct in some cases.

If you have a shower with limited extraction the humidity could be at 100% - not good for metal consumer units so not really suitable!

On the other hand, a well ventilated room, with a good cupboard/enclosure preventing high levels of moisture from getting to the consumer unit doesn't fall foul of the suitability issue.

I know this isn't a clear definitive answer, but it really does depend on the actual environment it's in.
 
First of all, rooms with just a toilet and basin are not classed as a special location, just “rooms containing a bath or shower”

The regs say everything in this special location has to be rcd protected, so this consumer unit may or may not be.

It’s not so much being able to be touch with wet hands, but how moisture in the air can affect the protective devices through corrosion.
The existing consumer unit is RCD protected, so hoping if i make an airtight cupboard around it to keep any moisture out i should be ok?
 
Unfortunately it isn't so clear cut.

There are restrictions for rooms containing a bath or shower, in Scotland this includes that switches (such as lights) are prohibited - although pull switches are OK.

However it has been established that anything in a fixed cupboard or enclosure is defined as not within the room. (So booster pumps etc can be underneath the bath tub as long as it's enclosed.) Also non-switching things such as fixed equipment like showers, macerator units etc are OK.

This means that there isn't any rule prohibiting consumer units inside a room containing a bath or shower, as long as its within some enclosure such as a cupboard.

However many people including some electricians just don't like it, and fall back on general "catch all" regulations such as "suitability for the environment " - which may be correct in some cases.

If you have a shower with limited extraction the humidity could be at 100% - not good for metal consumer units so not really suitable!

On the other hand, a well ventilated room, with a good cupboard/enclosure preventing high levels of moisture from getting to the consumer unit doesn't fall foul of the suitability issue.

I know this isn't a clear definitive answer, but it really does depend on the actual environment it's in.
Many thanks for the detailed reply, i think from what you've both said, it should be ok if i build an airtight cupboard around it, which will be a lot better than having to partition off the end of the room.
 
Many thanks for the detailed reply, i think from what you've both said, it should be ok if i build an airtight cupboard around it, which will be a lot better than having to partition off the end of the room.
Ultimately the electrician doing the work will have their own opinion and likes or dislikes, so check with them and if they are happy with what you are doing.
 
Is a 2 way consumer unit going to be adequate for a 1 bed flat?🤔
Hoping so,its mostly going to be lpg gas, hot water, heating from a combi, and then gas cooker also, so no real load of any sort electrical wise, but the electrician will confirm, can upgrade if needs be.
 
So this is a CU just for the garage being turned into a flat?
Is it going to still be supplied from the main house, or given a separate supply and meter?
 

Reply to Consumer unit in cupboard in Shower Room in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
761
One of our contractors has identified a concern with multiple showers on a single 100 amp supply.(unsure how many yet i have asked for further...
Replies
3
Views
204
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
798
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
581

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock